Three impedances, each of (3−4j) Ω, are connected in delta to a 200 V, three-phase, 50 Hz balanced supply. What are the values of line current and phase current, respectively, in the delta-connected load?
$ 40 \sqrt3 A and 40 A$
To find the line current and phase current in a delta-connected load, we first need to understand the relationship between line current, phase current, and the impedance in a delta connection.
The correct answer is: 40 \sqrt{3} A (line current) and 40 A (phase current).
For supplying a large three-phase load with neutral connection requirement, which transformer connection is generally preferred?
A three-phase, three winding Δ/Δ/Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is ___________. (Give the answer up to one decimal place.)
The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.
A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.
In Three Phase Transformer, The load Current is 139.1 A, and Secondary Voltage is 415 V. The Rating of the Transformer would be:
If the primary line voltage rating is 3.3 kV (Y side) of a 25 kVA, Y-Δ transformer (the per phase turns ratio is 5: 1), then the line current rating of the secondary side (in Ampere) is _________.