Question

For supplying a large three-phase load with neutral connection requirement, which transformer connection is generally preferred?

The correct answer is

Star-star connection with neutral grounding arrangement on both sides

To determine the most suitable transformer connection for supplying a large three-phase load with a neutral connection requirement, we need to evaluate the given options based on their characteristics and typical applications.

Options Analysis

  • Open delta connection for reduction of transformer copper losses: This configuration is typically used as an economical solution when one transformer is unavailable or fails. It does not provide a neutral connection and is not preferred for balanced large loads.
  • Delta-delta connection for single-phase domestic lighting systems: The delta-delta connection does not provide a neutral point, which is required for supplying single-phase loads with a neutral. This connection is common for purely three-phase loads without neutral requirements.
  • Scott connection for operation of balanced three-phase motor loads: The Scott connection is used for converting three-phase to two-phase systems, often not suited for providing a neutral point for three-phase loads.
  • Star-star connection with neutral grounding arrangement on both sides: The star-star (Y-Y) connection is advantageous for providing a neutral point on both the primary and secondary sides, which is crucial for supplying three-phase loads with neutral requirements. Neutral grounding helps stabilize voltage and improve safety.

Conclusion

The most appropriate transformer connection for supplying a large three-phase load with a neutral connection requirement is the Star-star (Y-Y) connection with neutral grounding arrangement on both sides. This configuration allows for a balanced load distribution, the availability of a neutral point, and enhanced safety through grounding.

Explanation

The star-star connection is particularly beneficial in scenarios where the load requires a neutral for single-phase connections or asymmetrical loads. Neutral grounding in this setup mitigates over-voltage risks and maintains system stability, making it a preferred choice for large, complex electrical systems that incorporate both three-phase and single-phase loads.

Hence, the correct answer is: Star-star connection with neutral grounding arrangement on both sides.

Was this answer helpful?

Similar Questions

  1. Three impedances, each of (3−4j) Ω, are connected in delta to a 200 V, three-phase, 50 Hz balanced supply. What are the values of line current and phase current, respectively, in the delta-connected load?


Important Questions from Three Phase Transformer Basics

  1. Three-phase transformer contains-

  2. Which type of connection is used for both large voltage and low voltage rating transformers?

  3. In Three Phase Transformer, The load Current is 139.1 A, and Secondary Voltage is 415 V. The Rating of the Transformer would be:

  4. The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.

  5. A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.

Need Expert Advice?
Test Series
RRB JE img
Railways
RRB JE Prev. Yr. Paper (CBT 1 + CBT 2) Test Series
290 Tests 5 Tests Free
4460 Attempts
4.3(88)
English

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App