A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.
192.45 V
Let's calculate the secondary line voltage of the three-phase transformer based on the given information.
We are given:
We need to find the secondary line voltage, \(V_{s,line}\), on no-load.
First, let's consider the primary winding which is connected in Star (Y). In a star connection, the relationship between line voltage and phase voltage is:
\[V_{line} = \sqrt{3} \times V_{phase}\]So, the primary phase voltage \(V_{p,phase}\) is:
\[V_{p,phase} = \frac{V_{p,line}}{\sqrt{3}} = \frac{1000}{\sqrt{3}}\]Next, the ratio of phase voltages in a transformer is equal to the ratio of turns:
\[\frac{V_{p,phase}}{V_{s,phase}} = \frac{N_p}{N_s}\]We can use this to find the secondary phase voltage \(V_{s,phase}\):
\[V_{s,phase} = V_{p,phase} \times \frac{N_s}{N_p}\] \[V_{s,phase} = \left(\frac{1000}{\sqrt{3}}\right) \times \left(\frac{200}{600}\right)\] \[V_{s,phase} = \left(\frac{1000}{\sqrt{3}}\right) \times \left(\frac{1}{3}\right)\] \[V_{s,phase} = \frac{1000}{3\sqrt{3}}\]Finally, let's consider the secondary winding which is connected in Delta (\(\Delta\)). In a delta connection, the relationship between line voltage and phase voltage is:
\[V_{line} = V_{phase}\]So, the secondary line voltage \(V_{s,line}\) is equal to the secondary phase voltage \(V_{s,phase}\).
\[V_{s,line} = V_{s,phase} = \frac{1000}{3\sqrt{3}}\]Now, let's calculate the numerical value:
\[V_{s,line} = \frac{1000}{3 \times \sqrt{3}} \approx \frac{1000}{3 \times 1.73205} \approx \frac{1000}{5.19615} \approx 192.45 \text{ V}\]Therefore, the secondary line voltage on no-load is approximately 192.45 V.
Three-phase transformer contains-
Consider three transformers in Δ - Δ, supplying their rated load. If one transformer is removed, then each of the remaining two transformers is overloaded. The overload on each transformer is given as
A three-phase, three winding Δ/Δ/Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is ___________. (Give the answer up to one decimal place.)
The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.
The most familiar application of zigzag transformer is