A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.

The correct answer is

192.45 V

Three-Phase Transformer Star-Delta Voltage Calculation

Let's calculate the secondary line voltage of the three-phase transformer based on the given information.

We are given:

  • Primary turns, \(N_p = 600\)
  • Secondary turns, \(N_s = 200\)
  • Primary supply line voltage, \(V_{p,line} = 1000\) V
  • Winding connection: Primary is Star (Y), Secondary is Delta (\(\Delta\))

We need to find the secondary line voltage, \(V_{s,line}\), on no-load.

First, let's consider the primary winding which is connected in Star (Y). In a star connection, the relationship between line voltage and phase voltage is:

\[V_{line} = \sqrt{3} \times V_{phase}\]

So, the primary phase voltage \(V_{p,phase}\) is:

\[V_{p,phase} = \frac{V_{p,line}}{\sqrt{3}} = \frac{1000}{\sqrt{3}}\]

Next, the ratio of phase voltages in a transformer is equal to the ratio of turns:

\[\frac{V_{p,phase}}{V_{s,phase}} = \frac{N_p}{N_s}\]

We can use this to find the secondary phase voltage \(V_{s,phase}\):

\[V_{s,phase} = V_{p,phase} \times \frac{N_s}{N_p}\] \[V_{s,phase} = \left(\frac{1000}{\sqrt{3}}\right) \times \left(\frac{200}{600}\right)\] \[V_{s,phase} = \left(\frac{1000}{\sqrt{3}}\right) \times \left(\frac{1}{3}\right)\] \[V_{s,phase} = \frac{1000}{3\sqrt{3}}\]

Finally, let's consider the secondary winding which is connected in Delta (\(\Delta\)). In a delta connection, the relationship between line voltage and phase voltage is:

\[V_{line} = V_{phase}\]

So, the secondary line voltage \(V_{s,line}\) is equal to the secondary phase voltage \(V_{s,phase}\).

\[V_{s,line} = V_{s,phase} = \frac{1000}{3\sqrt{3}}\]

Now, let's calculate the numerical value:

\[V_{s,line} = \frac{1000}{3 \times \sqrt{3}} \approx \frac{1000}{3 \times 1.73205} \approx \frac{1000}{5.19615} \approx 192.45 \text{ V}\]

Therefore, the secondary line voltage on no-load is approximately 192.45 V.

Was this answer helpful?

Important Questions from Three Phase Transformer Basics

  1. Three-phase transformer contains-

  2. Which type of connection is used for both large voltage and low voltage rating transformers?

  3. In Three Phase Transformer, The load Current is 139.1 A, and Secondary Voltage is 415 V. The Rating of the Transformer would be:

  4. The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.

  5. A three-phase, three winding Δ/Δ/Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is ___________. (Give the answer up to one decimal place.)

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App