Question

A three-phase, three winding Δ/Δ/Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is ___________. (Give the answer up to one decimal place.)

The loads consume720+j540 kVA and180+j240 kVA. Total complex power is900+j780 kVA, of magnitude1190.96599 kVA. Neglecting transformer losses, primary line current is \(I=|900+j780|/(\sqrt3\cdot1.1)=625.0950\ \mathrm A\), or 625.1 A.

Was this answer helpful?