A three-phase, three winding Δ/Δ/Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is ___________. (Give the answer up to one decimal place.)

Concept:

Power balance equation,

input kVA = output kVA

Explanation:

Equivalent circuit is given as,

using power balance equation,

input kVA = output kVA

kVA1 = kVA2 + kVA3

kVA1 = 900 ∠-36.87° + 300 ∠-53.13°

kVA1 = 720 - j 540 + 160 - j 240

kvA1 = 900 + j 780

kvA1 = 1190.9 ∠-40.9° kVA

We know that,

kVA = √3 Vl Il

where,

Vl = line voltage

Il = line current

Now,

\(\rm kVA=\sqrt{3}V_{l_1}I_{l_1}=1190.9\angle-40.9^\circ\)

⇒ \(I_{l_1}=\frac{1190.9\angle-40.9\ \rm kVA}{\sqrt{3}\times1.1\ \rm kV}\)

⇒ \(\rm I_{l_1}=625.09\angle-40.9^\circ\ \rm A\)

Hence,

        RMS line current drawn by the 1.1 kV winding from the mains is 625.09 A

Was this answer helpful?

Important Questions from Three Phase Transformer Basics

  1. Three-phase transformer contains-

  2. Which type of connection is used for both large voltage and low voltage rating transformers?

  3. In Three Phase Transformer, The load Current is 139.1 A, and Secondary Voltage is 415 V. The Rating of the Transformer would be:

  4. The core of a three-phase, 50 Hz, 1000/400 V delta/star: 300 kVA core type transformer operated with a flux of 0.04 wb. Find the EMF per turn.

  5. A three-phase transformer has 600 primary turns and 200 secondary turns. If the supply voltage is 1000 V, find the secondary line voltage on no-load when the windings are connected in star–delta.

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App