A domestic MCCB is marked 25A, 6 kA, 230V AC. Which fault current will this MCCB safely interrupt?

This question was previously asked in
RRB ALP 2025 CBT 2 Wiremen Question Paper (28-Jul-2026) (Shift 2)
The correct answer is

Any fault current up to 6,000 A

To solve this question, we need to understand the specifications on the MCCB (Molded Case Circuit Breaker) and what they signify:

  1. Rated Current (25A): This is the maximum load current the MCCB can carry without tripping. It indicates that the MCCB can handle continuous currents up to 25 amperes without operating (i.e., tripping).

  2. Breaking Capacity (6 kA): The breaking capacity, or interrupting capacity, defines the maximum fault current that the MCCB can safely interrupt without damage. Therefore, an MCCB marked with 6 kA can interrupt fault currents up to 6,000 amperes safely.

  3. Nominal Voltage (230V AC): This indicates the standard voltage for which the MCCB is designed to operate. Here, 230 volts is the supply voltage for which the device is suitable.

Now, analyzing the options:

  • Option A: "Any current at 230 V AC" - This is incorrect because it does not consider the limits of fault current or overload.
  • Option B: "Any fault current up to 6,000 A" - This matches the breaking capacity specification of 6 kA, thus is correct.
  • Option C: "Any overload up to 25 A" - Incorrect, as overload relates to operating current, not fault interruption capacity.
  • Option D: "Any short-circuit above 25A" - This is incorrect. Fault interruption refers to the ability to interrupt short-circuits up to the breaking capacity, not just above 25A.

Therefore, the MCCB can safely interrupt "Any fault current up to 6,000 A". Thus, the correct answer is:

Any fault current up to 6,000 A

Was this answer helpful?

Similar Questions

  1. L series MCBs can be used effectively in:

  2. Fusing factor of fuse is always

  3. Which component in an MCB is responsible for detecting a short circuit?

  4. A shunt release in an MCCB is commonly used for:
  5. A single device that ensures efficient protection from electrical hazard of shock and fire caused by over current, short circuit, earth leakage, and earth fault is:

  6. What is used as a Circuit breaker?
  7. Which component in a wiring diagram is specifically used to protect against overcurrent?

  8. Which statement best describes an isolating switch?

  9. If an ELCB in a domestic installation trips occasionally without any apparent fault, what could be a probable reason?

  10. An industrial panel uses a cartridge fuse rated at 250V, 32A. If a technician replaces it with a 16A fuse of the same voltage rating, what is the likely outcome during normal operation at 28A?


Important Questions from Circuit Breakers

  1. L series MCBs can be used effectively in:

  2. Fusing factor of fuse is always

  3. What is one of the functions of circuit breakers in a substation?

  4. For below 400 KV systems, the circuit breaker is designed to withstand ______above the normal system voltage.
  5. If Ic is the critical current and Zo is the surge impedance, the basic impulse insulation level can be calculated as

Need Expert Advice?
Upcoming Exams
RRB Technician
October 06, 2026
RRB JE
October 27, 2026
RRB ALP
November 03, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
1083 Attempts
4.3(239)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App