Which safety device is designed to detect cable electrical leakage and disconnect the circuit?
Earth leakage circuit breaker
Detecting leakage relies on the principle that, in a healthy circuit, the current leaving through the live conductor exactly returns through the neutral; any difference means current is escaping to earth.
An earth leakage circuit breaker continuously compares the live and neutral currents, and when it senses an imbalance, indicating current is leaking to earth through faulty insulation or a person, it trips and disconnects the circuit within milliseconds.
A fuse simply melts when the current exceeds a set value, so it reacts only to overload or short-circuit, not to a small leakage that never raises the total current.
A miniature circuit breaker likewise trips on overcurrent, whether overload or short-circuit, and cannot recognise the balanced-versus-unbalanced condition that signals leakage.
A relay is a general control and switching element operated by another signal; on its own it is not designed to sense earth leakage.
Only the device that measures the live-neutral imbalance responds specifically to leakage, making it the correct protective device here.
Hence, the answer is Earth leakage circuit breaker.
L series MCBs can be used effectively in:
Fusing factor of fuse is always
A single device that ensures efficient protection from electrical hazard of shock and fire caused by over current, short circuit, earth leakage, and earth fault is:
An industrial panel uses a cartridge fuse rated at 250V, 32A. If a technician replaces it with a 16A fuse of the same voltage rating, what is the likely outcome during normal operation at 28A?
Which component in an MCB is responsible for detecting a short circuit?
Which part of a Vacuum Circuit Breaker (VCB) helps to maintain insulation and protects the breaker from external environmental influences?
Which type of MCB tripping curve is most appropriate for protecting standard domestic lighting circuits?
Which component in a wiring diagram is specifically used to protect against overcurrent?
L series MCBs can be used effectively in:
Fusing factor of fuse is always
If Ic is the critical current and Zo is the surge impedance, the basic impulse insulation level can be calculated as
Which of the following is the merit of circuit breakers?