Question

Which safety device is designed to detect cable electrical leakage and disconnect the circuit?

This question was previously asked in
RRB NTPC 2025 Graduate Level CBT 1 Question Paper (25-Mar-2026) (Shift 3)
The correct answer is

Earth leakage circuit breaker

Detecting leakage relies on the principle that, in a healthy circuit, the current leaving through the live conductor exactly returns through the neutral; any difference means current is escaping to earth.

An earth leakage circuit breaker continuously compares the live and neutral currents, and when it senses an imbalance, indicating current is leaking to earth through faulty insulation or a person, it trips and disconnects the circuit within milliseconds.

A fuse simply melts when the current exceeds a set value, so it reacts only to overload or short-circuit, not to a small leakage that never raises the total current.

A miniature circuit breaker likewise trips on overcurrent, whether overload or short-circuit, and cannot recognise the balanced-versus-unbalanced condition that signals leakage.

A relay is a general control and switching element operated by another signal; on its own it is not designed to sense earth leakage.

Only the device that measures the live-neutral imbalance responds specifically to leakage, making it the correct protective device here.

Hence, the answer is Earth leakage circuit breaker.

Was this answer helpful?

Similar Questions

  1. Which component in a wiring diagram is specifically used to protect against overcurrent?

  2. Which statement best describes an isolating switch?

  3. A domestic MCCB is marked 25A, 6 kA, 230V AC. Which fault current will this MCCB safely interrupt?

  4. If an ELCB in a domestic installation trips occasionally without any apparent fault, what could be a probable reason?

  5. Which part of a Vacuum Circuit Breaker (VCB) helps to maintain insulation and protects the breaker from external environmental influences?

  6. An industrial panel uses a cartridge fuse rated at 250V, 32A. If a technician replaces it with a 16A fuse of the same voltage rating, what is the likely outcome during normal operation at 28A?

  7. Which type of MCB tripping curve is most appropriate for protecting standard domestic lighting circuits?


Important Questions from Circuit Breakers

  1. A single device that ensures efficient protection from electrical hazard of shock and fire caused by over current, short circuit, earth leakage, and earth fault is:

  2. L series MCBs can be used effectively in:

  3. An ON-OFF switch with overload protection is called a _______.

  4. When an electric device, appliance or electrical installation is connected to the earth electrode without a fuse, circuit breaker or resistance/Impedance, It is called ___________.

  5. What is the most common and important type of fuse used in domestic application?

Need Expert Advice?
Upcoming Exams
RRB NTPC
September 27, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
741 Attempts
4.3(233)
English, Hindi
More Questions from RRB ALP

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App