All Exams Test series for 1 year @ ₹349 only
Question

Which type of MCB tripping curve is most appropriate for protecting standard domestic lighting circuits?

This question was previously asked in
RRB ALP 2025 CBT 2 Wiremen Question Paper (28-Jul-2026) (Shift 2)
The correct answer is

Type B MCB

Miniature circuit breakers are classified by tripping curves that describe how many times the rated current must flow before the magnetic element trips instantaneously, matching the breaker to the inrush behaviour of the load.

A Type B MCB trips magnetically at about three to five times its rated current, which is ideal for circuits with little switch-on surge such as domestic lighting and general-purpose socket outlets.

Because lighting and resistive loads draw only a small initial current, the low Type B threshold gives fast protection against faults without nuisance tripping.

A Type C MCB trips at about five to ten times rated current, chosen for moderately inductive loads like small motors and fluorescent banks, so it is less sensitive than needed for plain lighting.

A Type D MCB trips at about ten to twenty times rated current, suited to high-inrush loads such as transformers and large motors, far more than a lighting circuit requires.

Type A is a very sensitive curve used mainly for semiconductor and measuring circuits and is not a standard general-purpose domestic type.

Hence, the answer is Type B MCB.

Was this answer helpful?

Similar Questions

  1. L series MCBs can be used effectively in:

  2. Fusing factor of fuse is always

  3. A single device that ensures efficient protection from electrical hazard of shock and fire caused by over current, short circuit, earth leakage, and earth fault is:

  4. What is used as a Circuit breaker?
  5. An industrial panel uses a cartridge fuse rated at 250V, 32A. If a technician replaces it with a 16A fuse of the same voltage rating, what is the likely outcome during normal operation at 28A?

  6. Which component in a wiring diagram is specifically used to protect against overcurrent?

  7. Which statement best describes an isolating switch?

  8. A domestic MCCB is marked 25A, 6 kA, 230V AC. Which fault current will this MCCB safely interrupt?

  9. If an ELCB in a domestic installation trips occasionally without any apparent fault, what could be a probable reason?

  10. Which component in an MCB is responsible for detecting a short circuit?


Important Questions from Circuit Breakers

  1. L series MCBs can be used effectively in:

  2. Fusing factor of fuse is always

  3. For below 400 KV systems, the circuit breaker is designed to withstand ______above the normal system voltage.
  4. If Ic is the critical current and Zo is the surge impedance, the basic impulse insulation level can be calculated as

  5. Which of the following is the merit of circuit breakers?

Need Expert Advice?
Upcoming Exams
RRB JE
October 27, 2026
RRB ALP
November 03, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
1297 Attempts
4.3(246)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App