All Exams Test series for 1 year @ ₹349 only
Question

Which of the following statement are correct for PI controller?

A. PI controller increases the system type by 1, therefore it improves the steady state error by one order.

B. PI controller reduce the rise time

C. PI controller increase the bandwidth.

D. PI controller is a high pass filter.

E. PI controller adds a pole at S=0 to the forward path transfer function, hence type of system increased by 1.

Choose the most appropriate answer from the options given below :

This question was previously asked in
UGC NET 2023 Electronic Science Question Paper (13-Dec-2023) (Shift 1)
The correct answer is

A and E only

The PI controller.

\(G_c(s)=K_p+\dfrac{K_i}{s}=\dfrac{K_p s+K_i}{s}\)

It therefore contributes one pole at the origin and one finite zero at \(s=-K_i/K_p\). Everything in the question follows from that.

E — "PI adds a pole at s = 0, hence the type increases by 1." TRUE. The system type is by definition the number of poles at the origin in the open-loop transfer function, so inserting 1/s raises it by one.

A — "PI increases the type by 1, therefore improves the steady-state error by one order." TRUE. Steady-state error depends on the static error constants:

\(e_{ss}(\text{step})=\dfrac{1}{1+K_p},\qquad e_{ss}(\text{ramp})=\dfrac{1}{K_v}\)

Raising the type from 0 to 1 makes \(K_p \to \infty\), so the step error becomes zero instead of finite; a Type-1 plant becomes Type-2 and tracks a ramp with zero error. This elimination of offset is the whole purpose of integral action.

B — "PI reduces the rise time." FALSE. Integral action is sluggish: it accumulates error over time, so the closed-loop response becomes slower and generally more oscillatory. The rise time increases and the overshoot tends to grow. (It is derivative action, PD, that speeds up the transient.)

C — "PI increases the bandwidth." FALSE. The 1/s term boosts low-frequency gain while contributing −90° of phase; this is lag-type compensation, which reduces the gain-crossover frequency and hence narrows the bandwidth. Slower response and reduced bandwidth are two statements of the same fact.

D — "PI is a high-pass filter." FALSE. Its magnitude is largest at low frequency (infinite at d.c.) and falls to Kp at high frequency — that is low-pass / lag behaviour. This also gives PI the useful side effect of attenuating high-frequency measurement noise.

Summary of the trade-off. PI buys zero steady-state error at the price of slower response, less bandwidth and reduced relative stability — which is why PID adds derivative action to recover the speed.

Hence, the correct answer is A and E only.

Was this answer helpful?

Similar Questions

  1. Match List I with List II

    LIST I (Transfer function) LIST II (Controller)
    A.$\frac{K_{1}S + K_{2} + K_{3}S^{2}}{S}$I.P-controller
    B.K1II.PI-controller
    C.$\frac{K_1S + K_2}{S}$III.PD-controller
    D.K1 + K2SIV.PID - controller

    Choose the correct answer from the options given below:

  2. The value of Kp in Proportional, PI, PID, controllers are given

    A. For proportional Kp = T/L

    B. For PI, Kp = 0.9 T/L

    C. For PI, Kp = 1.7 T/L

    D. For PID, Kp = 1.2 T/L

    E. For PID Kp = 0.9 T/L

    Choose the correct answer from the options given below:

  3. The pole-zero configuration of a PI controller is represented by

  4. Read the following statements regarding PID controller :

    (a) The system complexity of a PID controller is less than that of a PI controller.

    (b) A PID controller produces no action for any constant error signal.

    (c) A PID controller is used to increase the damping factor of the dominant poles of a PI controlled system.

    (d) A PID controller is used to decrease the damping factor of the dominant poles of a PI controlled system.

    Which of the above statements are correct ?

  5. Assertion (A) : A PI controller introduces a pole in the system thereby increasing the order and type of system by one.

    Reason (R) : The increase in the type of the system ensures a decrease in the steady state error of the system.

    Select your answer using the codes given below.

  6. Consider the following controllers for their system complexity and arrange them in increasing order of complexity.

    (A) Proportional controller
    (B) Proportional plus derivative controller
    (C) Proportional plus integral plus derivative controller
    (D) Proportional plus integral

    Choose the most appropriate answer from the options given below :


Important Questions from Controllers

  1. Match List I with List II

    LIST I (Transfer function) LIST II (Controller)
    A.$\frac{K_{1}S + K_{2} + K_{3}S^{2}}{S}$I.P-controller
    B.K1II.PI-controller
    C.$\frac{K_1S + K_2}{S}$III.PD-controller
    D.K1 + K2SIV.PID - controller

    Choose the correct answer from the options given below:

  2. The value of Kp in Proportional, PI, PID, controllers are given

    A. For proportional Kp = T/L

    B. For PI, Kp = 0.9 T/L

    C. For PI, Kp = 1.7 T/L

    D. For PID, Kp = 1.2 T/L

    E. For PID Kp = 0.9 T/L

    Choose the correct answer from the options given below:

  3. The pole-zero configuration of a PI controller is represented by

  4. Read the following statements regarding PID controller :

    (a) The system complexity of a PID controller is less than that of a PI controller.

    (b) A PID controller produces no action for any constant error signal.

    (c) A PID controller is used to increase the damping factor of the dominant poles of a PI controlled system.

    (d) A PID controller is used to decrease the damping factor of the dominant poles of a PI controlled system.

    Which of the above statements are correct ?

  5. The plant in the feedback control system shown in the figure is $P(s) = \frac{a}{s^2-b^2}$, where $a>0$ and $b>0$. The type(s) of controller $C(s)$ that CANNOT stabilize the plant is/are

Need Expert Advice?
Upcoming Exams
CTET
December 12, 2026
CBSE UGC NET
December 14, 2026
CSIR UGC NET
December 19, 2026
Test Series
UGC NET img
Teaching
UGC NET (Paper 2) 2026 Mock Test Series
796 Tests 2 Tests Free
4.4(40)
English
More Questions from UGC NET

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App