What will be the eddy current loss if the supply frequency of a transformer becomes double?

This question was previously asked in
RRB NTPC 2024 Undergraduate CBT 1 Question Paper (29-Aug-2025) (Shift 1)
The correct answer is

Four times

Eddy current losses in a transformer are proportional to the square of the supply frequency and the square of the magnetic flux density. The formula for eddy current loss is given by:

\(P_e = K f^2 B^2 t^2\)

where:

  • \(P_e\) is the eddy current loss
  • \(K\) is a constant that depends on the material properties and geometry of the core
  • \(f\) is the supply frequency
  • \(B\) is the magnetic flux density
  • \(t\) is the thickness of the lamination

If the supply frequency (\(f\)) is doubled, while other factors remain constant, the eddy current loss will change as follows:

Original loss: \(P_{e1} = K (f)^2 B^2 t^2\)

New loss with doubled frequency: \(P_{e2} = K (2f)^2 B^2 t^2 = 4 K (f)^2 B^2 t^2 = 4 P_{e1}\)

Therefore, the eddy current loss will become four times its original value.

Was this answer helpful?

Similar Questions

  1. Which power loss is assessed by open-circuit test on transformer?

Important Questions from Transformer Core Losses

  1. The lamination thickness of a rotor should be selected from _______ to minimize the eddy current loss.

  2. Which power loss is assessed by open-circuit test on transformer?
  3. Eddy current loss in a transformer can be reduced by _________.

  4. Stray load-losses in a motor vary according to square of the load current; are caused by the leakage flux induced by load currents in laminations and account for 4% to 5% of total losses. What is the way to reduce these losses?

  5. The core loss of a single phase, 230/115 V, 50Hz power transformer is measured from 230 V side by feeding the primary (230 V side) from a variable voltage variable frequency source while keeping the secondary open circuited. The core loss is measured to be 1050 W for 230 V, 50 Hz input. The core loss is gain measured to be 500 W for 138 V, 30 Hz input. The hysteresis and eddy current losses of the transformer for 230 V, 50 Hz input are respectively

Need Expert Advice?
Upcoming Exams
RRB NTPC
September 27, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
893 Attempts
4.3(235)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App