What will be the eddy current loss if the supply frequency of a transformer becomes double?

This question was previously asked in
RRB NTPC 2024 Undergraduate CBT 1 Question Paper (29-Aug-2025) (Shift 1)
The correct answer is

Four times

Eddy current losses in a transformer are proportional to the square of the supply frequency and the square of the magnetic flux density. The formula for eddy current loss is given by:

\(P_e = K f^2 B^2 t^2\)

where:

  • \(P_e\) is the eddy current loss
  • \(K\) is a constant that depends on the material properties and geometry of the core
  • \(f\) is the supply frequency
  • \(B\) is the magnetic flux density
  • \(t\) is the thickness of the lamination

If the supply frequency (\(f\)) is doubled, while other factors remain constant, the eddy current loss will change as follows:

Original loss: \(P_{e1} = K (f)^2 B^2 t^2\)

New loss with doubled frequency: \(P_{e2} = K (2f)^2 B^2 t^2 = 4 K (f)^2 B^2 t^2 = 4 P_{e1}\)

Therefore, the eddy current loss will become four times its original value.

Was this answer helpful?

Similar Questions

  1. Which power loss is assessed by open-circuit test on transformer?

Important Questions from Transformer Core Losses

  1. Which power loss is assessed by open-circuit test on transformer?
  2. Eddy current loss in a transformer can be reduced by _________.

  3. Stray load-losses in a motor vary according to square of the load current; are caused by the leakage flux induced by load currents in laminations and account for 4% to 5% of total losses. What is the way to reduce these losses?

  4. A single-phase, 4 kVA, 200 V/100 V, 50 Hz transformer with laminated CRGO steel core has rated no-load loss of 450 W. When the high-voltage winding is excited with 160 V, 40 Hz sinusoidal ac supply, the no-load losses are found to be 320 W. When the high-voltage winding of the same transformer is supplied from a 100 V, 25 Hz sinusoidal ac source, the no-load losses will be_________ W (rounded off to 2 decimal places).

  5. For a single phase, two winding transformer, the supply frequency and voltage are both increased by 10%. The percentage changes in the hysteresis loss and eddy current loss, respectively, are

Need Expert Advice?
Upcoming Exams
RRB Technician
October 06, 2026
RRB JE
October 27, 2026
RRB ALP
November 03, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
1082 Attempts
4.3(238)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App