Out of the following, which loss is also a category of magnetic losses?
In electrical machines, various types of energy losses occur, reducing efficiency. These losses can be broadly categorized into core losses (or iron losses), copper losses, and mechanical losses. Magnetic losses fall under the category of core losses.
Core losses, also known as iron losses, occur in the magnetic core (stator and rotor cores) of electrical machines due to the alternating magnetic flux. These losses are generally considered constant for a given flux density and frequency. The two main types of core losses are:
Let's examine the other options provided:
Based on the definitions above:
Therefore, out of the given options, eddy current loss is classified as a magnetic loss.
Eddy current loss in a transformer can be reduced by _________.
Stray load-losses in a motor vary according to square of the load current; are caused by the leakage flux induced by load currents in laminations and account for 4% to 5% of total losses. What is the way to reduce these losses?
A single-phase, 4 kVA, 200 V/100 V, 50 Hz transformer with laminated CRGO steel core has rated no-load loss of 450 W. When the high-voltage winding is excited with 160 V, 40 Hz sinusoidal ac supply, the no-load losses are found to be 320 W. When the high-voltage winding of the same transformer is supplied from a 100 V, 25 Hz sinusoidal ac source, the no-load losses will be_________ W (rounded off to 2 decimal places).
For a single phase, two winding transformer, the supply frequency and voltage are both increased by 10%. The percentage changes in the hysteresis loss and eddy current loss, respectively, are
Transformer at no-load behaves like: