At full load copper loss and iron loss of transformer are 6300 W and 2500 W respectively. The copper loss and iron loss at two-third load will be respectively?

The correct answer is

2800 W and 2500 W

Understanding the behavior of losses in a transformer at different load conditions is crucial for power system analysis and efficiency calculations. Transformers experience two main types of losses: copper losses and iron losses.

Transformer Loss Components Explained

  • Copper Loss (\(P_{cu}\)): This loss occurs in the windings due to the resistance of the copper wire. It is also known as \(I^2R\) loss. Copper loss is directly dependent on the square of the current flowing through the windings. As the load on the transformer changes, the current drawn also changes, leading to a change in copper loss. Specifically, if the load is \(x\) times the full load, the current will be \(x\) times the full load current, and thus the copper loss will be \(x^2\) times the full load copper loss.
  • Iron Loss (\(P_{i}\)): Also known as core loss, this loss occurs in the magnetic core of the transformer. Iron loss is primarily composed of hysteresis loss and eddy current loss. These losses depend on the maximum flux density in the core and the supply frequency. Since the transformer is usually operated at a constant supply voltage and frequency, the flux density in the core remains almost constant from no-load to full-load conditions. Therefore, iron loss is considered to be constant, irrespective of the load.

Full Load Loss Data Provided

We are given the following information about the transformer at full load:

  • Full load copper loss (\(P_{cu,full}\)) = 6300 W
  • Full load iron loss (\(P_{i,full}\)) = 2500 W

Calculating Transformer Losses at Two-Third Load

We need to determine the copper loss and iron loss when the transformer is operating at two-third (\(2/3\)) of its full load.

Iron Loss Calculation at Two-Third Load

As previously explained, the iron loss in a transformer remains constant regardless of the load variation, assuming constant supply voltage and frequency.

Therefore, the iron loss at two-third load will be the same as the full load iron loss:

\[ P_{i,2/3} = P_{i,full} \] \[ P_{i,2/3} = 2500 \text{ W} \]

Copper Loss Calculation at Two-Third Load

Copper loss is directly proportional to the square of the load fraction. In this case, the load fraction \(x\) is \(2/3\).

The formula for copper loss at a fraction of full load is:

\[ P_{cu,x} = x^2 \times P_{cu,full} \]

Substituting the given values into the formula:

\[ P_{cu,2/3} = \left(\frac{2}{3}\right)^2 \times P_{cu,full} \] \[ P_{cu,2/3} = \frac{4}{9} \times 6300 \text{ W} \]

Now, perform the multiplication:

\[ P_{cu,2/3} = 4 \times \frac{6300}{9} \text{ W} \] \[ P_{cu,2/3} = 4 \times 700 \text{ W} \] \[ P_{cu,2/3} = 2800 \text{ W} \]

Summary of Transformer Losses at Two-Third Load

Based on our calculations, the copper loss and iron loss at two-third load for the transformer are:

  • Copper loss = 2800 W
  • Iron loss = 2500 W

Thus, the copper loss and iron loss at two-third load are 2800 W and 2500 W respectively.

Was this answer helpful?

Important Questions from Transformer Core Losses

  1. A ferrite core has less eddy current loss than an iron core because ferrites have

  2. If the transformer frequency is changed from 50 Hz to 60 Hz, the ratio of eddy current loss at 60 Hz to 50 Hz at constant voltage will be:

  3. The lamination thickness of a rotor should be selected from _______ to minimize the eddy current loss.

  4. Eddy current loss in a transformer can be reduced by _________.

  5. Out of the following, which loss is also a category of magnetic losses?

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App