For a single phase, two winding transformer, the supply frequency and voltage are both increased by 10%. The percentage changes in the hysteresis loss and eddy current loss, respectively, are

The correct answer is

10 and 21

V/f stays constant, hence peak flux density is unchanged. Hysteresis loss scales with f, increasing10%; eddy-current loss scales with f², increasing1.1²−1=21%. Thus 10%,21%.