For a system with 230 V AC, 5 A current and lag of 30°, what's the reactive power?
575 VAR
The question asks for the reactive power of a system given the voltage, current, and the phase angle between them. Reactive power is a key component of AC power systems and is measured in Volt-Ampere Reactive (VAR).
We are provided with the following information:
A lagging phase angle typically indicates an inductive load.
In an AC circuit, the reactive power (Q) is calculated using the formula:
\[Q = V \times I \times \sin(\phi)\]
Where:
Using the given values, we can substitute them into the formula:
Given: \(V = 230\,V\), \(I = 5\,A\), \(\phi = 30^\circ\)
First, find the sine of the phase angle:
\[\sin(30^\circ) = 0.5\]
Now, plug the values into the reactive power formula:
\[Q = 230\,V \times 5\,A \times \sin(30^\circ)\]
\[Q = 230 \times 5 \times 0.5\]
\[Q = 1150 \times 0.5\]
\[Q = 575\]
The reactive power is 575 VAR.
The calculated reactive power is 575 VAR. Reactive power is associated with the energy stored and returned by reactive components like inductors and capacitors. In a lagging power factor scenario (as indicated by the lag of 30°), the reactive power is inductive.
Let's compare our calculated value with the given options:
| Option | Value |
|---|---|
| 1 | 275 VAR |
| 2 | 675 VAR |
| 3 | 175 VAR |
| 4 | 575 VAR |
Our calculated value of 575 VAR matches Option 4.
Reactive power is the portion of AC power that does not result in useful work. It flows back and forth between the source and the load. Inductive loads (like motors and transformers) consume lagging reactive power, while capacitive loads (like capacitors) supply leading reactive power. Managing reactive power is important for maintaining voltage stability and efficiency in power transmission and distribution systems.
| Concept | Symbol | Formula | Unit | Description |
|---|---|---|---|---|
| Apparent Power | S | \[S = V \times I\] | VA (Volt-Ampere) | Total power supplied by the source |
| Real Power (Active Power) | P | \[P = V \times I \times \cos(\phi)\] | W (Watt) | Power consumed and converted to useful work |
| Reactive Power | Q | \[Q = V \times I \times \sin(\phi)\] | VAR (Volt-Ampere Reactive) | Power exchanged between source and reactive components |
| Power Factor | pf | \[\cos(\phi) = \frac{P}{S}\] | Dimensionless | Ratio of real power to apparent power |
The relationship between apparent power (S), real power (P), and reactive power (Q) can be visualized using the power triangle. It's a right-angled triangle where:
The Pythagorean relationship holds:
\[S^2 = P^2 + Q^2\]
The angle between apparent power (S) and real power (P) is the power factor angle (\(\phi\)).
Understanding the power triangle helps in analyzing and improving the power factor of electrical systems.
If voltage is measured across an AC mains open switch, the meter will read:
What is the relation between line voltage and phase voltage in a delta connection?
If the value of phase voltage in a star connected circuit is 240 V, then its line voltage is ______.
A sinusoidal alternating voltage of 50 Hz has an RMS value of 200 V. Find the maximum value and wavelength.
In which of the following connections do we have common neutral point?
What is meant by line voltage?
If apparent power is found equal to active power, then the system power factor is:
When a capacitor load is connected, the power factor is:
When an inductive load is connected, the power factor is:
To find real power, the apparent power has to be multiplied by:
If voltage is measured across an AC mains open switch, the meter will read:
What is the phase difference between the line voltage and phase voltage in a star-connected load?
What is the relation between line voltage and phase voltage in a delta connection?