When an inductive load is connected, the power factor is:

This question was previously asked in
RRB ALP 2018 CBT 2 Fitter Question Paper (21-Jan-2019) (Shift 3)
The correct answer is

Lagging

Understanding Power Factor in AC Circuits

The power factor is a crucial concept in alternating current (AC) circuits. It represents the ratio of true power (or real power) consumed by a load to the apparent power delivered to the circuit. It is a measure of how effectively electrical power is being converted into useful work output.

Mathematically, the power factor (PF) is defined as the cosine of the phase angle (\(\phi\)) between the voltage and current waveforms:

\[ \text{PF} = \cos(\phi) \]

The value of the power factor ranges from 0 to 1.

What is an Inductive Load?

An inductive load is an electrical load that primarily consists of components that store energy in a magnetic field when electric current flows. Common examples include:

  • Electric motors
  • Transformers
  • Inductors (coils)
  • Fluorescent lamp ballasts

These components have inductance (L), which opposes changes in current.

Voltage and Current Relationship in Inductive Loads

In a purely inductive AC circuit, the current lags behind the voltage by 90 degrees (\(\pi/2\) radians). When an inductive load is connected in a real-world AC circuit (which also has some resistance), the current still lags the voltage, but by an angle less than 90 degrees (typically between 0 and 90 degrees).

This phase difference (\(\phi\)) is positive for an inductive load, meaning the current waveform reaches its peak value after the voltage waveform reaches its peak value.

Power Factor for an Inductive Load: Lagging

Since the current lags the voltage in an inductive load, the phase angle (\(\phi\)) is positive. The power factor is \(\cos(\phi)\). When the current lags the voltage, the power factor is described as "lagging".

Here's a summary of load types and power factors:

Load Type Voltage-Current Phase Relationship Phase Angle (\(\phi\)) Power Factor Description
Purely Resistive In phase \(0^\circ\) Unity (\(\cos(0^\circ)=1\))
Purely Inductive Current lags voltage by \(90^\circ\) \(90^\circ\) Zero lagging (\(\cos(90^\circ)=0\))
Purely Capacitive Current leads voltage by \(90^\circ\) \(-90^\circ\) Zero leading (\(\cos(-90^\circ)=0\))
Inductive (R-L) Current lags voltage (by \(0^\circ < \phi < 90^\circ\)) Positive Lagging (\(0 < \text{PF} < 1\))
Capacitive (R-C) Current leads voltage (by \(-90^\circ < \phi < 0^\circ\)) Negative Leading (\(0 < \text{PF} < 1\))

Therefore, when an inductive load is connected, the power factor is lagging.

Revision Table: Key Concepts of Power Factor

Concept Description
Power Factor (PF) Ratio of true power to apparent power (\(\text{PF} = \cos(\phi)\))
True Power (P) Power consumed by resistance, measured in Watts (W)
Apparent Power (S) Total power supplied, product of voltage and current, measured in Volt-Amperes (VA)
Reactive Power (Q) Power stored and returned by reactive components (inductors, capacitors), measured in Volt-Ampere Reactive (VAR)
Phase Angle (\(\phi\)) Angle between voltage and current waveforms

Additional Information on Power Factor and Inductive Loads

A lagging power factor due to inductive loads is common in industrial and residential settings because of the prevalence of motors, transformers, and other inductive equipment. A low lagging power factor can be undesirable for several reasons:

  • It increases the total current drawn from the source for the same amount of useful power, leading to higher energy losses in transmission lines and equipment.
  • It requires larger conductors and transformers to handle the increased current.
  • It can result in voltage drops in the system.

To improve a lagging power factor, power factor correction techniques are often used. The most common method is to connect capacitors in parallel with the inductive load. Capacitors draw leading reactive power, which can counteract the lagging reactive power drawn by the inductive load, bringing the overall power factor closer to unity.

Was this answer helpful?

Similar Questions

  1. The ratio of resistance to impedance is ______.

  2. If voltage is measured across an AC mains open switch, the meter will read:

  3. What is the relation between line voltage and phase voltage in a delta connection?

  4. If the value of phase voltage in a star connected circuit is 240 V, then its line voltage is ______.

  5. A sinusoidal alternating voltage of 50 Hz has an RMS value of 200 V. Find the maximum value and wavelength.

  6. In which of the following connections do we have common neutral point?

  7. What is meant by line voltage?

  8. If apparent power is found equal to active power, then the system power factor is:

  9. When a capacitor load is connected, the power factor is:

  10. To find real power, the apparent power has to be multiplied by:


Important Questions from Alternating Current

  1. The ratio of resistance to impedance is ______.

  2. If voltage is measured across an AC mains open switch, the meter will read:

  3. The phase voltage of a star-connected, three-phase circuit is 200 V. The line voltage will be

  4. What is the phase difference between the line voltage and phase voltage in a star-connected load?

  5. Which of the following correctly represents the standard nominal voltage and frequency for alternating current (AC) power distribution in India?
Need Expert Advice?
Upcoming Exams
RRB NTPC
September 27, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
893 Attempts
4.3(235)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App