Question

A 1 hp motor is used for running a dual cylinder reciprocating compressor of a refrigeration system based on R-134a refrigerant having 185 kJ $kg^{-1}$ cooling capacity. COP of the system is 4.2 and overall efficiency of the compressor is 80%. Specific volume of the refrigerant vapour at suction temperature is 0.15 $m^3$ $kg^{-1}$. The compressor with bore diameters of 40 mm each runs at 1440 rpm.

The mass flow rate of the refrigerant in kg $min^{-1}$ is

The correct answer is
0.813

Compressor Mass Flow Rate Calculation

This problem requires calculating the mass flow rate ($\dot{m}$) of the refrigerant. We are given the motor power, compressor efficiency, refrigerant cooling capacity, COP, and specific volume. The most direct method uses the power and efficiency information.

Step 1: Determine Brake Power and Indicated Power

  • The motor power is given as 1 hp. Convert this to kilowatts (kW): $P_B = 1 \text{ hp} \times 0.746 \text{ kW/hp} = 0.746 \text{ kW}$ This is the brake power ($P_B$) delivered to the compressor shaft.
  • The overall efficiency ($\eta_{overall}$) relates indicated power ($P_{ind}$) to brake power ($P_B$): $P_{ind} = \eta_{overall} \times P_B$
  • Given $\eta_{overall} = 80\% = 0.8$: $P_{ind} = 0.8 \times 0.746 \text{ kW} = 0.5968 \text{ kW}$ The indicated power is the power actually used to compress the refrigerant.

Step 2: Calculate Net Work Input per kg

  • The Coefficient of Performance (COP) relates cooling capacity ($Q_L$) to the net work input ($W_{net}$): $COP = \frac{Q_L}{W_{net}}$
  • Rearranging to find the net work input per kg: $W_{net} = \frac{Q_L}{COP}$
  • Given $Q_L = 185 \text{ kJ/kg}$ and $COP = 4.2$: $W_{net} = \frac{185 \text{ kJ/kg}}{4.2} \approx 44.0476 \text{ kJ/kg}$

Step 3: Calculate Mass Flow Rate

  • The indicated power is the product of the mass flow rate and the net work done per unit mass: $P_{ind} = \dot{m} \times W_{net}$ Note: Ensure units are consistent. We'll use Watts (W) for power and Joules (J) for work.
  • Convert indicated power to Watts: $P_{ind} = 0.5968 \text{ kW} = 0.5968 \times 1000 \text{ W} = 596.8 \text{ J/s}$
  • Convert net work to Joules per kg: $W_{net} = 44.0476 \text{ kJ/kg} = 44.0476 \times 1000 \text{ J/kg} = 44047.6 \text{ J/kg}$
  • Calculate mass flow rate ($\dot{m}$) in kg/s: $\dot{m} = \frac{P_{ind}}{W_{net}} = \frac{596.8 \text{ J/s}}{44047.6 \text{ J/kg}} \approx 0.013549 \text{ kg/s}$
  • Convert mass flow rate to kg/min: $\dot{m}_{\text{min}} = \dot{m}_{\text{sec}} \times 60 \text{ s/min}$ $\dot{m}_{\text{min}} = 0.013549 \text{ kg/s} \times 60 \text{ s/min} \approx 0.81294 \text{ kg/min}$

Therefore, the mass flow rate of the refrigerant is approximately 0.813 kg/min.

Note: The specific volume and compressor dimensions were not needed for this calculation path, which relies on power and efficiency metrics.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  5. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App