Compressor Mass Flow Rate Calculation
This problem requires calculating the mass flow rate ($\dot{m}$) of the refrigerant. We are given the motor power, compressor efficiency, refrigerant cooling capacity, COP, and specific volume. The most direct method uses the power and efficiency information.
Step 1: Determine Brake Power and Indicated Power
- The motor power is given as 1 hp. Convert this to kilowatts (kW):
$P_B = 1 \text{ hp} \times 0.746 \text{ kW/hp} = 0.746 \text{ kW}$
This is the brake power ($P_B$) delivered to the compressor shaft.
- The overall efficiency ($\eta_{overall}$) relates indicated power ($P_{ind}$) to brake power ($P_B$):
$P_{ind} = \eta_{overall} \times P_B$
- Given $\eta_{overall} = 80\% = 0.8$:
$P_{ind} = 0.8 \times 0.746 \text{ kW} = 0.5968 \text{ kW}$
The indicated power is the power actually used to compress the refrigerant.
Step 2: Calculate Net Work Input per kg
- The Coefficient of Performance (COP) relates cooling capacity ($Q_L$) to the net work input ($W_{net}$):
$COP = \frac{Q_L}{W_{net}}$
- Rearranging to find the net work input per kg:
$W_{net} = \frac{Q_L}{COP}$
- Given $Q_L = 185 \text{ kJ/kg}$ and $COP = 4.2$:
$W_{net} = \frac{185 \text{ kJ/kg}}{4.2} \approx 44.0476 \text{ kJ/kg}$
Step 3: Calculate Mass Flow Rate
- The indicated power is the product of the mass flow rate and the net work done per unit mass:
$P_{ind} = \dot{m} \times W_{net}$
Note: Ensure units are consistent. We'll use Watts (W) for power and Joules (J) for work.
- Convert indicated power to Watts:
$P_{ind} = 0.5968 \text{ kW} = 0.5968 \times 1000 \text{ W} = 596.8 \text{ J/s}$
- Convert net work to Joules per kg:
$W_{net} = 44.0476 \text{ kJ/kg} = 44.0476 \times 1000 \text{ J/kg} = 44047.6 \text{ J/kg}$
- Calculate mass flow rate ($\dot{m}$) in kg/s:
$\dot{m} = \frac{P_{ind}}{W_{net}} = \frac{596.8 \text{ J/s}}{44047.6 \text{ J/kg}} \approx 0.013549 \text{ kg/s}$
- Convert mass flow rate to kg/min:
$\dot{m}_{\text{min}} = \dot{m}_{\text{sec}} \times 60 \text{ s/min}$
$\dot{m}_{\text{min}} = 0.013549 \text{ kg/s} \times 60 \text{ s/min} \approx 0.81294 \text{ kg/min}$
Therefore, the mass flow rate of the refrigerant is approximately 0.813 kg/min.
Note: The specific volume and compressor dimensions were not needed for this calculation path, which relies on power and efficiency metrics.