A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to

The correct answer is
$84.40$

Carnot Refrigeration Heat Rejection Calculation

This solution calculates the heat rejected by a refrigeration system operating on a reverse Carnot cycle.

Given Parameters

  • Cold Reservoir Temperature, $T_L = -30\text{ }^\circ\text{C}$
  • Hot Reservoir Temperature, $T_H = 20\text{ }^\circ\text{C}$
  • Refrigeration Capacity, $Q_L = 70\text{ kW}$

Temperature Conversion

Convert the temperatures from Celsius to Kelvin:

  • $T_L (\text{K}) = -30 + 273.15 = 243.15\text{ K}$
  • $T_H (\text{K}) = 20 + 273.15 = 293.15\text{ K}$

Heat Rejected Calculation

For a reverse Carnot cycle, the ratio of heat absorbed ($Q_L$) to heat rejected ($Q_H$) is equal to the ratio of the absolute temperatures of the cold reservoir ($T_L$) and the hot reservoir ($T_H$).

The formula is:

$ \frac{Q_L}{Q_H} = \frac{T_L}{T_H} $

Rearranging the formula to solve for $Q_H$:

$ Q_H = Q_L \times \frac{T_H}{T_L} $

Substitute the given values:

$ Q_H = 70\text{ kW} \times \frac{293.15\text{ K}}{243.15\text{ K}} $

Calculate the value:

$ Q_H = 70 \times 1.20563\text{ kW} $ $ Q_H \approx 84.394\text{ kW} $

Result

The heat rejected at the condenser is approximately $84.394\text{ kW}$. This value is nearest to $84.40\text{ kW}$.

Was this answer helpful?

Important Questions from Refrigeration

  1. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  2. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  3. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  4. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
  5. In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8 °C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ $kg^{-1}$ $K^{-1}$. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ $kg^{-1}$. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App