Question

In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.

The correct answer is
19.13, 14.99

The problem asks for the power required by the compressors in a cascade refrigeration system. We are given the COPs of the two stages, the tonnage associated with the "cooling cycle", and a relationship between heat rejection and heat absorption.

Cascade System Parameters

Based on the structure of cascade systems and the provided options matching the calculations, we interpret the given parameters as follows:

  • The "cooling cycle" refers to the upper refrigeration stage.
  • The "cascade" refers to the lower refrigeration stage.
  • COP of the upper stage ($COP_{upper}$) = 3.7
  • COP of the lower stage ($COP_{lower}$) = 4.2
  • The tonnage of the cooling cycle ($Q_{evap, upper}$) = 15 TR.
  • The relation: Heat absorbed by the lower stage evaporator ($Q_{evap, lower}$) is 70% of the heat rejected by the upper stage condenser ($Q_{cond, upper}$).
  • Conversion factors: 1 TR = 3.52 kW, 1 hp = 0.746 kW.

Cooling Compressor Power Calculation

First, convert the cooling capacity from TR to kW:

$ Q_{evap, upper} = 15 \text{ TR} \times 3.52 \frac{\text{kW}}{\text{TR}} = 52.8 \text{ kW} $

Next, calculate the power required by the upper stage compressor (referred to as the "cooling compressor") using its COP:

$ W_{upper} = \frac{Q_{evap, upper}}{COP_{upper}} = \frac{52.8 \text{ kW}}{3.7} \approx 14.2703 \text{ kW} $

Convert this power to horsepower (hp):

$ W_{upper} (\text{hp}) = \frac{14.2703 \text{ kW}}{0.746 \frac{\text{kW}}{\text{hp}}} \approx 19.1289 \text{ hp} $

So, the power required by the cooling compressor is approximately 19.13 hp.

Cascade Compressor Power Calculation

Calculate the total heat rejected by the upper stage condenser:

$ Q_{cond, upper} = Q_{evap, upper} + W_{upper} = 52.8 \text{ kW} + 14.2703 \text{ kW} \approx 67.0703 \text{ kW} $

The problem states that the cascade (lower stage) removes 70% of this heat. This heat is absorbed by the lower stage evaporator:

$ Q_{evap, lower} = 0.70 \times Q_{cond, upper} = 0.70 \times 67.0703 \text{ kW} \approx 46.9492 \text{ kW} $

Now, calculate the power required by the lower stage compressor (referred to as the "cascade compressor") using its COP:

$ W_{lower} = \frac{Q_{evap, lower}}{COP_{lower}} = \frac{46.9492 \text{ kW}}{4.2} \approx 11.1784 \text{ kW} $

Convert this power to horsepower (hp):

$ W_{lower} (\text{hp}) = \frac{11.1784 \text{ kW}}{0.746 \frac{\text{kW}}{\text{hp}}} \approx 14.9845 \text{ hp} $

So, the power required by the cascade compressor is approximately 14.99 hp.

Conclusion

The powers required by the cooling and cascade compressors are approximately 19.13 hp and 14.99 hp, respectively.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  3. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  4. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
  5. In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8 °C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ $kg^{-1}$ $K^{-1}$. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ $kg^{-1}$. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App