The problem asks for the power required by the compressors in a cascade refrigeration system. We are given the COPs of the two stages, the tonnage associated with the "cooling cycle", and a relationship between heat rejection and heat absorption.
Based on the structure of cascade systems and the provided options matching the calculations, we interpret the given parameters as follows:
First, convert the cooling capacity from TR to kW:
$ Q_{evap, upper} = 15 \text{ TR} \times 3.52 \frac{\text{kW}}{\text{TR}} = 52.8 \text{ kW} $
Next, calculate the power required by the upper stage compressor (referred to as the "cooling compressor") using its COP:
$ W_{upper} = \frac{Q_{evap, upper}}{COP_{upper}} = \frac{52.8 \text{ kW}}{3.7} \approx 14.2703 \text{ kW} $
Convert this power to horsepower (hp):
$ W_{upper} (\text{hp}) = \frac{14.2703 \text{ kW}}{0.746 \frac{\text{kW}}{\text{hp}}} \approx 19.1289 \text{ hp} $
So, the power required by the cooling compressor is approximately 19.13 hp.
Calculate the total heat rejected by the upper stage condenser:
$ Q_{cond, upper} = Q_{evap, upper} + W_{upper} = 52.8 \text{ kW} + 14.2703 \text{ kW} \approx 67.0703 \text{ kW} $
The problem states that the cascade (lower stage) removes 70% of this heat. This heat is absorbed by the lower stage evaporator:
$ Q_{evap, lower} = 0.70 \times Q_{cond, upper} = 0.70 \times 67.0703 \text{ kW} \approx 46.9492 \text{ kW} $
Now, calculate the power required by the lower stage compressor (referred to as the "cascade compressor") using its COP:
$ W_{lower} = \frac{Q_{evap, lower}}{COP_{lower}} = \frac{46.9492 \text{ kW}}{4.2} \approx 11.1784 \text{ kW} $
Convert this power to horsepower (hp):
$ W_{lower} (\text{hp}) = \frac{11.1784 \text{ kW}}{0.746 \frac{\text{kW}}{\text{hp}}} \approx 14.9845 \text{ hp} $
So, the power required by the cascade compressor is approximately 14.99 hp.
The powers required by the cooling and cascade compressors are approximately 19.13 hp and 14.99 hp, respectively.