A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are

The correct answer is
25.4 and 32.5

Chiller Power Consumption & Tonnage Calculation

This solution calculates the electric motor power consumption in kW and the refrigeration tonnage (TR) required for cooling milk using a mechanical vapour compression chiller.

Step 1: Calculate Total Heat Removed

The total heat ($Q$) removed from the milk is calculated using the formula:

$Q = m \times c_p \times \Delta T$

  • Mass of milk ($m$): $12500$ kg
  • Specific heat ($c_p$): $3.8$ kJ kg$^{-1}$ K$^{-1}$
  • Temperature change ($\Delta T$): $30 \,^{\circ}\text{C} - 4 \,^{\circ}\text{C} = 26 \,^{\circ}\text{C}$ (or 26 K)

$Q = 12500 \text{ kg} \times 3.8 \text{ kJ kg}^{-1} \text{ K}^{-1} \times 26 \text{ K} = 1,235,000 \text{ kJ}$

Step 2: Calculate Cooling Load in kW

The cooling load is the rate of heat removal. Convert the total heat removed over the given time into kW.

Cooling Load ($P_{cooling}$) = $\frac{Q}{\text{time in seconds}}$

  • Time: $3$ hours $= 3 \times 3600 = 10800$ seconds

$P_{cooling} = \frac{1,235,000 \text{ kJ}}{10800 \text{ s}} \approx 114.35 \text{ kW}$

Step 3: Calculate Motor Power Consumption

The power consumed by the motor is related to the cooling load by the Coefficient of Performance (COP).

Power Consumed ($P_{motor}$) = $\frac{P_{cooling}}{\text{COP}}$

  • COP: $4.5$

$P_{motor} = \frac{114.35 \text{ kW}}{4.5} \approx 25.41 \text{ kW}$

Step 4: Calculate Tonnage of Refrigeration (TR)

Convert the cooling load from kW to Tons of Refrigeration (TR). The standard conversion factor is approximately $1 \text{ TR} = 3.517 \text{ kW}$.

Tonnage (TR) = $\frac{P_{cooling}}{3.517 \text{ kW/TR}}$

Tonnage = $\frac{114.35 \text{ kW}}{3.517 \text{ kW/TR}} \approx 32.51 \text{ TR}$

Conclusion

The calculated power consumed by the electric motor is approximately $25.4$ kW, and the tonnage of refrigeration is approximately $32.5$ TR. This corresponds to Option 1.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  5. In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8 °C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ $kg^{-1}$ $K^{-1}$. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ $kg^{-1}$. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App