This solution calculates the electric motor power consumption in kW and the refrigeration tonnage (TR) required for cooling milk using a mechanical vapour compression chiller.
The total heat ($Q$) removed from the milk is calculated using the formula:
$Q = m \times c_p \times \Delta T$
$Q = 12500 \text{ kg} \times 3.8 \text{ kJ kg}^{-1} \text{ K}^{-1} \times 26 \text{ K} = 1,235,000 \text{ kJ}$
The cooling load is the rate of heat removal. Convert the total heat removed over the given time into kW.
Cooling Load ($P_{cooling}$) = $\frac{Q}{\text{time in seconds}}$
$P_{cooling} = \frac{1,235,000 \text{ kJ}}{10800 \text{ s}} \approx 114.35 \text{ kW}$
The power consumed by the motor is related to the cooling load by the Coefficient of Performance (COP).
Power Consumed ($P_{motor}$) = $\frac{P_{cooling}}{\text{COP}}$
$P_{motor} = \frac{114.35 \text{ kW}}{4.5} \approx 25.41 \text{ kW}$
Convert the cooling load from kW to Tons of Refrigeration (TR). The standard conversion factor is approximately $1 \text{ TR} = 3.517 \text{ kW}$.
Tonnage (TR) = $\frac{P_{cooling}}{3.517 \text{ kW/TR}}$
Tonnage = $\frac{114.35 \text{ kW}}{3.517 \text{ kW/TR}} \approx 32.51 \text{ TR}$
The calculated power consumed by the electric motor is approximately $25.4$ kW, and the tonnage of refrigeration is approximately $32.5$ TR. This corresponds to Option 1.