First, determine the total heat that needs to be removed from the potato mass.
The total heat load ($Q_{load}$) is calculated using the formula:
$Q_{load} = m \times c_p \times \Delta T$ $Q_{load} = 10000 \text{ kg} \times 3.2 \text{ kJ } kg^{-1} K^{-1} \times 22 \text{ K} = 704000 \text{ kJ}$Next, find the required cooling capacity (rate of heat extraction) in kW.
The required cooling capacity ($Q_{rate}$) is:
$Q_{rate} = \frac{Q_{load}}{t}$ $Q_{rate} = \frac{704000 \text{ kJ}}{21600 \text{ s}} \approx 32.59 \text{ kJ/s} = 32.59 \text{ kW}$Calculate the mass flow rate of the refrigerant needed to achieve the required cooling capacity.
The refrigerant flow rate ($\dot{m}_{ref}$) is:
$\dot{m}_{ref} = \frac{Q_{rate}}{L_{evap}}$ $\dot{m}_{ref} = \frac{32.59 \text{ kW}}{210 \text{ kJ/kg}} = \frac{32.59 \text{ kJ/s}}{210 \text{ kJ/kg}} \approx 0.155 \text{ kg/s}$Convert the flow rate to kg per minute:
$\dot{m}_{ref} (\text{kg/min}) = 0.155 \text{ kg/s} \times 60 \text{ s/min} \approx 9.3 \text{ kg/min}$Finally, calculate the power required by the compressor.
The compressor power ($W_{comp}$) is determined using the COP formula:
$COP = \frac{\text{Cooling Effect}}{\text{Work Input}} = \frac{Q_{rate}}{W_{comp}}$ $W_{comp} = \frac{Q_{rate}}{COP}$ $W_{comp} = \frac{32.59 \text{ kW}}{4.2} \approx 7.76 \text{ kW}$Therefore, the refrigerant flow rate is approximately 9.3 kg/min and the compressor power requirement is approximately 7.76 kW.