Question

In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8 °C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ $kg^{-1}$ $K^{-1}$. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ $kg^{-1}$. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be

The correct answer is
9.3 kg $min^{-1}$; 7.76 kW

Calculating Potato Cooling Load

First, determine the total heat that needs to be removed from the potato mass.

  • Mass of potato ($m$): $10 \text{ metric ton} = 10 \times 1000 \text{ kg} = 10000 \text{ kg}$
  • Initial temperature ($T_1$): $30 \text{ °C}$
  • Final temperature ($T_2$): $8 \text{ °C}$
  • Temperature change ($\Delta T$): $T_1 - T_2 = 30 \text{ °C} - 8 \text{ °C} = 22 \text{ °C}$ (or $22 \text{ K}$)
  • Specific heat capacity ($c_p$): $3.2 \text{ kJ } kg^{-1} K^{-1}$

The total heat load ($Q_{load}$) is calculated using the formula:

$Q_{load} = m \times c_p \times \Delta T$ $Q_{load} = 10000 \text{ kg} \times 3.2 \text{ kJ } kg^{-1} K^{-1} \times 22 \text{ K} = 704000 \text{ kJ}$

Determining Refrigeration Capacity

Next, find the required cooling capacity (rate of heat extraction) in kW.

  • Total time ($t$): $6 \text{ hours} = 6 \times 3600 \text{ s} = 21600 \text{ s}$

The required cooling capacity ($Q_{rate}$) is:

$Q_{rate} = \frac{Q_{load}}{t}$ $Q_{rate} = \frac{704000 \text{ kJ}}{21600 \text{ s}} \approx 32.59 \text{ kJ/s} = 32.59 \text{ kW}$

Calculating Refrigerant Flow Rate

Calculate the mass flow rate of the refrigerant needed to achieve the required cooling capacity.

  • Evaporator load extraction capacity ($L_{evap}$): $210 \text{ kJ/kg}$

The refrigerant flow rate ($\dot{m}_{ref}$) is:

$\dot{m}_{ref} = \frac{Q_{rate}}{L_{evap}}$ $\dot{m}_{ref} = \frac{32.59 \text{ kW}}{210 \text{ kJ/kg}} = \frac{32.59 \text{ kJ/s}}{210 \text{ kJ/kg}} \approx 0.155 \text{ kg/s}$

Convert the flow rate to kg per minute:

$\dot{m}_{ref} (\text{kg/min}) = 0.155 \text{ kg/s} \times 60 \text{ s/min} \approx 9.3 \text{ kg/min}$

Determining Compressor Power Requirement

Finally, calculate the power required by the compressor.

  • Coefficient of Performance (COP): $4.2$

The compressor power ($W_{comp}$) is determined using the COP formula:

$COP = \frac{\text{Cooling Effect}}{\text{Work Input}} = \frac{Q_{rate}}{W_{comp}}$ $W_{comp} = \frac{Q_{rate}}{COP}$ $W_{comp} = \frac{32.59 \text{ kW}}{4.2} \approx 7.76 \text{ kW}$

Therefore, the refrigerant flow rate is approximately 9.3 kg/min and the compressor power requirement is approximately 7.76 kW.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  5. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App