Motor Horse Power Calculation for Refrigerator

This solution explains how to calculate the motor horse power required for a refrigerator compressor based on its performance metrics.

Given Parameters

  • Coefficient of Performance (COP) = $4.5$
  • Heat extracted during evaporation ($Q_{evap}$) = $200 kJ kg-1$
  • Refrigerant flow rate ($\dot{m}$) = $1.5 kg min-1$

Calculating Cooling Rate

First, determine the total cooling rate ($Q_{rate}$) provided by the refrigerator. Convert the flow rate from kg/min to kg/s:

$\dot{m} = 1.5 \frac{\text{kg}}{\text{min}} \times \frac{1 \text{ min}}{60 \text{ s}} = 0.025 \frac{\text{kg}}{\text{s}}$

Calculate the cooling rate:

$Q_{rate} = Q_{evap} \times \dot{m} = 200 \frac{\text{kJ}}{\text{kg}} \times 0.025 \frac{\text{kg}}{\text{s}} = 5 \frac{\text{kJ}}{\text{s}} = 5 \text{ kW}$

Calculating Compressor Work Rate

The Coefficient of Performance (COP) relates the cooling effect to the work input required.

$COP = \frac{\text{Cooling Effect}}{\text{Work Input}}$

Calculate the work rate ($W_{rate}$) needed by the compressor:

$W_{rate} = \frac{Q_{rate}}{COP} = \frac{5 \text{ kW}}{4.5} \approx 1.111 \text{ kW}$

Converting Work Rate to Horse Power

Convert the work rate from kilowatts (kW) to horse power (HP). The conversion factor is approximately $1 \text{ HP} = 0.746 \text{ kW}$.

$HP = \frac{W_{rate}}{0.746 \frac{\text{kW}}{\text{HP}}} = \frac{1.111 \text{ kW}}{0.746 \frac{\text{kW}}{\text{HP}}} \approx 1.49 \text{ HP}$

Rounding to the nearest option, the required horse power is approximately 1.5 HP.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  4. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
  5. In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8 °C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ $kg^{-1}$ $K^{-1}$. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ $kg^{-1}$. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App