Calculate Cooling Load
First, determine the total heat that needs to be removed from the potatoes. This is the sensible heat due to the temperature change.
- Mass of potato: $m = 100 \text{ metric tons} = 100 \times 1000 \text{ kg} = 1 \times 10^5 \text{ kg}$
- Temperature change: $\Delta T = 35 \text{ °C} - 8 \text{ °C} = 27 \text{ °C}$
- Specific heat capacity: $c_p = 3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$
- Total heat to remove: $Q = m \times c_p \times \Delta T$
- $Q = (1 \times 10^5 \text{ kg}) \times (3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}) \times (27 \text{ °C}) = 8.37 \times 10^6 \text{ kJ}$
Calculate Refrigeration Capacity
Next, find the rate at which this heat must be removed over the given time period. This is the refrigeration capacity.
- Time: $t = 5 \text{ hours}$
- Cooling load rate: $\dot{Q}_L = Q / t$
- $\dot{Q}_L = (8.37 \times 10^6 \text{ kJ}) / (5 \text{ hours}) = 1.674 \times 10^6 \text{ kJ/hour}$
- Convert to kW: $1 \text{ kJ/hour} = 1/3600 \text{ kW}$
- $\dot{Q}_L = (1.674 \times 10^6 \text{ kJ/hour}) / 3600 \text{ s/hour} \approx 465 \text{ kW}$
Determine Refrigerant Flow Rate
The cooling capacity is provided by the refrigerant vaporizing. Use the latent heat of vaporization to find the mass flow rate of the refrigerant.
- Latent heat of vaporization: $h_{fg} = 230 \text{ kJ kg}^{-1}$
- Refrigerant flow rate: $\dot{m}_{ref} = \dot{Q}_L / h_{fg}$
- $\dot{m}_{ref} = (465 \text{ kJ/s}) / (230 \text{ kJ kg}^{-1}) \approx 2.0217 \text{ kg/s}$
- Convert to kg/min: $\dot{m}_{ref} = 2.0217 \text{ kg/s} \times 60 \text{ s/min} \approx 121.3 \text{ kg min}^{-1}$
Calculate Compressor Power Input
Use the Coefficient of Performance (COP) to find the power input required by the compressor.
- COP: $COP = 3.66$
- Power input: $P_{in} = \dot{Q}_L / COP$
- $P_{in} = (465 \text{ kW}) / 3.66 \approx 127.1 \text{ kW}$
The calculated values are approximately $121.3 \text{ kg min}^{-1}$ for the refrigerant flow rate and $127.1 \text{ kW}$ for the power input.