All Exams Test series for 1 year @ ₹349 only
Question

A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are

The correct answer is
$121.3 \text{ kg min}^{-1}$ and $127.1 \text{ kW}$

Calculate Cooling Load

First, determine the total heat that needs to be removed from the potatoes. This is the sensible heat due to the temperature change.

  • Mass of potato: $m = 100 \text{ metric tons} = 100 \times 1000 \text{ kg} = 1 \times 10^5 \text{ kg}$
  • Temperature change: $\Delta T = 35 \text{ °C} - 8 \text{ °C} = 27 \text{ °C}$
  • Specific heat capacity: $c_p = 3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$
  • Total heat to remove: $Q = m \times c_p \times \Delta T$
  • $Q = (1 \times 10^5 \text{ kg}) \times (3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}) \times (27 \text{ °C}) = 8.37 \times 10^6 \text{ kJ}$

Calculate Refrigeration Capacity

Next, find the rate at which this heat must be removed over the given time period. This is the refrigeration capacity.

  • Time: $t = 5 \text{ hours}$
  • Cooling load rate: $\dot{Q}_L = Q / t$
  • $\dot{Q}_L = (8.37 \times 10^6 \text{ kJ}) / (5 \text{ hours}) = 1.674 \times 10^6 \text{ kJ/hour}$
  • Convert to kW: $1 \text{ kJ/hour} = 1/3600 \text{ kW}$
  • $\dot{Q}_L = (1.674 \times 10^6 \text{ kJ/hour}) / 3600 \text{ s/hour} \approx 465 \text{ kW}$

Determine Refrigerant Flow Rate

The cooling capacity is provided by the refrigerant vaporizing. Use the latent heat of vaporization to find the mass flow rate of the refrigerant.

  • Latent heat of vaporization: $h_{fg} = 230 \text{ kJ kg}^{-1}$
  • Refrigerant flow rate: $\dot{m}_{ref} = \dot{Q}_L / h_{fg}$
  • $\dot{m}_{ref} = (465 \text{ kJ/s}) / (230 \text{ kJ kg}^{-1}) \approx 2.0217 \text{ kg/s}$
  • Convert to kg/min: $\dot{m}_{ref} = 2.0217 \text{ kg/s} \times 60 \text{ s/min} \approx 121.3 \text{ kg min}^{-1}$

Calculate Compressor Power Input

Use the Coefficient of Performance (COP) to find the power input required by the compressor.

  • COP: $COP = 3.66$
  • Power input: $P_{in} = \dot{Q}_L / COP$
  • $P_{in} = (465 \text{ kW}) / 3.66 \approx 127.1 \text{ kW}$

The calculated values are approximately $121.3 \text{ kg min}^{-1}$ for the refrigerant flow rate and $127.1 \text{ kW}$ for the power input.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
  5. In a cold storage, 10 metric ton of potato is to be brought down from 30 to 8 °C storage temperature in 6 hours of air blast at the evaporator temperature of -10°C. Specific heat capacity of potato is 3.2 kJ $kg^{-1}$ $K^{-1}$. COP of the refrigeration cycle deployed is 4.2 with evaporator load extraction capacity of 210 kJ $kg^{-1}$. Neglecting the respiration load of potato, the refrigerant flow rate and compressor power requirement will be
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App