The condition of refrigerant at the exit of the compressor in a vapor compression refrigeration system is:

The correct answer is
Superheated vapor

Compressor Exit Refrigerant State Explained

In a vapor compression refrigeration system, the compressor plays a crucial role in increasing the pressure and temperature of the refrigerant. Understanding the condition of the refrigerant at the exit of the compressor is key to analyzing the system's performance.

Vapor Compression Cycle Overview

The basic vapor compression cycle involves four main processes:

  • Evaporation: Refrigerant absorbs heat and becomes low-pressure vapor.
  • Compression: The low-pressure vapor is compressed into high-pressure, high-temperature vapor.
  • Condensation: Refrigerant rejects heat and turns into high-pressure liquid.
  • Expansion: High-pressure liquid expands to low pressure.

Compressor Function and Refrigerant State Change

The compressor takes in low-pressure refrigerant vapor from the evaporator. Its primary job is to increase the refrigerant's pressure significantly. This process requires energy input (work), which not only raises the pressure but also substantially increases the temperature of the refrigerant vapor.

Because the temperature rises well above the saturation temperature corresponding to the high pressure achieved, the refrigerant at the exit of the compressor is always in a state of superheated vapor.

Analysis of Options

Let's examine the given options for the refrigerant's condition at the compressor exit:

  • Saturated liquid: This is incorrect. Liquid states occur after the condenser and before the expansion valve.
  • Wet vapor: This is a mixture of liquid and vapor. While a compressor might sometimes receive vapor close to saturation, the compression process itself heats it beyond saturation.
  • Dry saturated vapor: This represents vapor at its saturation temperature and pressure. Compression raises the temperature above this point.
  • Superheated vapor: This is vapor at a temperature higher than its saturation temperature for the given pressure. This accurately describes the condition of the refrigerant after being compressed in a standard vapor compression refrigeration system.

Conclusion on Compressor Exit Condition

The process of compression in a refrigeration system involves adding work to the refrigerant vapor, leading to a significant increase in both its pressure and temperature. This results in the refrigerant leaving the compressor as superheated vapor, ready to move to the condenser.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  5. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App