Question

A 1 hp motor is used for running a dual cylinder reciprocating compressor of a refrigeration system based on R-134a refrigerant having 185 kJ $kg^{-1}$ cooling capacity. COP of the system is 4.2 and overall efficiency of the compressor is 80%. Specific volume of the refrigerant vapour at suction temperature is 0.15 $m^3$ $kg^{-1}$. The compressor with bore diameters of 40 mm each runs at 1440 rpm.

The compressor stroke length in mm is

The correct answer is
33.7

The problem asks for the stroke length of a dual cylinder reciprocating compressor. We are given the motor power, cooling capacity, COP, compressor efficiency, specific volume, bore diameter, and speed.

Motor Power Conversion

First, convert the motor power from horsepower (hp) to kilowatts (kW). Assuming 1 hp = 745.7 W:

$P_{motor} = 1 \text{ hp} \times 745.7 \text{ W/hp} = 745.7 \text{ W}$

Convert watts to kilowatts:

$P_{motor} = 745.7 \text{ W} \times \frac{1 \text{ kW}}{1000 \text{ W}} = 0.7457 \text{ kW}$

Specific Work Calculation

The Coefficient of Performance (COP) relates the cooling capacity ($q_L$, specific refrigerating effect) to the ideal work input ($w_{ideal}$) per unit mass.

$COP = \frac{q_L}{w_{ideal}}$

Rearranging to find the ideal specific work:

$w_{ideal} = \frac{q_L}{COP} = \frac{185 \text{ kJ/kg}}{4.2} \approx 44.05 \text{ kJ/kg}$

The overall efficiency ($\eta_{overall}$) relates the ideal specific work to the actual specific work ($w_{actual}$) required at the compressor shaft.

$\eta_{overall} = \frac{w_{ideal}}{w_{actual}}$

Calculate the actual specific work:

$w_{actual} = \frac{w_{ideal}}{\eta_{overall}} = \frac{44.05 \text{ kJ/kg}}{0.80} \approx 55.06 \text{ kJ/kg}$

Mass Flow Rate Determination

The motor power input is equal to the mass flow rate ($\dot{m}$) multiplied by the actual specific work ($w_{actual}$).

$P_{motor} = \dot{m} \times w_{actual}$

Solve for the mass flow rate:

$\dot{m} = \frac{P_{motor}}{w_{actual}} = \frac{0.7457 \text{ kW}}{55.06 \text{ kJ/kg}} = \frac{0.7457 \text{ kJ/s}}{55.06 \text{ kJ/kg}} \approx 0.01354 \text{ kg/s}$

Suction Volume Rate Calculation

The actual volume flow rate ($V_g$) entering the compressor is the mass flow rate multiplied by the specific volume ($v_g$) at suction conditions.

$V_g = \dot{m} \times v_g = 0.01354 \text{ kg/s} \times 0.15 \text{ m}^3/\text{kg} \approx 0.002031 \text{ m}^3/\text{s}$

Stroke Length Calculation

The displacement volume rate ($V_d$) of the compressor is calculated using its dimensions and speed.

$V_d = n_{cyl} \times \frac{\pi}{4} D^2 L \times N_{strokes/sec}$

Where:

  • $n_{cyl} = 2$ (dual cylinder)
  • $D = 40 \text{ mm} = 0.04 \text{ m}$ (bore diameter)
  • $N = 1440 \text{ rpm} = \frac{1440}{60} = 24 \text{ strokes/s}$
  • $L$ is the stroke length in meters.

Substitute the values:

$V_d = 2 \times \frac{\pi}{4} (0.04 \text{ m})^2 \times L \times 24 \text{ s}^{-1}$

$V_d = 2 \times \frac{\pi}{4} \times 0.0016 \text{ m}^2 \times L \times 24 \text{ s}^{-1} \approx 0.060317 L \text{ m}^3/\text{s}$ (where L is in meters)

The actual volume flow rate ($V_g$) must be equal to the displacement volume rate ($V_d$) if volumetric efficiency is assumed to be 1 (i.e., $V_g = V_d$).

$0.002031 \text{ m}^3/\text{s} = 0.060317 L$

Solve for $L$:

$L = \frac{0.002031}{0.060317} \approx 0.03367 \text{ m}$

Convert the stroke length to millimeters:

$L \approx 0.03367 \text{ m} \times 1000 \text{ mm/m} \approx 33.67 \text{ mm}$

This value is approximately 33.7 mm.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  5. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App