A single-phase preventer continuously monitors and protects preferably which motor against phase failure?

This question was previously asked in
RRB JE 2025 CBT 2 Mechanical and Allied Engg Question Paper English (2-Jul-2026) (Shift-1)
The correct answer is

3-phase induction motor

A single-phase preventer is a device used to monitor and protect three-phase motors, specifically the 3-phase induction motor, from phase failure or phase loss. Here's how and why:

  1. Concept of Phase Failure:
    • Phase failure in a three-phase motor occurs when one of the supply phases is lost or is significantly lower in voltage than the other two.
    • This results in unequal phase currents and can cause severe motor heating and damage due to unbalanced operation.
  2. Working of a Single-Phase Preventer:
    • A single-phase preventer detects the loss of any phase or unbalanced condition in the supply.
    • It then disconnects the motor from the power supply to prevent damage.
    • Additionally, it may trigger an alarm or indicator signal to alert the operator of the fault condition.
  3. Why Other Motors are Not Monitored by Single-Phase Preventers:
    • DC Motor: Operates on direct current; hence, phase failure does not apply.
    • Reluctance Motor: Typically, single-phase or small three-phase, not often used in applications requiring phase failure prevention.
    • Single-phase Induction Motor: Naturally operates on a single phase, so phase failure protection is not applicable.

Conclusion: Among the options provided, the 3-phase induction motor is the only one that requires a single-phase preventer for protection against phase failure. This makes it the correct answer.

Was this answer helpful?

Similar Questions

  1. Which of the following sets of statements about the causes of errors in current transformers is correct?

     i) Leakage reactance in secondary winding contributes to ratio error

     ii) High magnetizing current increases phase angle error

     iii) Burden with low power factor increases phase angle error

     iv) Core saturation reduces both ratio and phase angle errors

  2. Consider the following statements about torque in synchronous motors. 

    I. The torque in a synchronous motor is produced only when the rotor is locked into synchronism. 

    II. The torque is directly proportional to the sine of the load angle (δ). 

    III. Synchronous motor develops starting torque proportional to the power input. 

    IV. Maximum torque occurs at δ = 180°. 

    Which of the above statements are correct?

  3. Which of the following is a key maintenance practice for reliable operation of a 3-phase induction motor?

  4. If the frequency of an AC source is doubled, the impedance of a pure resistor ____________.


Important Questions from Three Phase Induction Motor

  1. Which of the following starters is not meant for starting of d.c. motor ?
  2. A change of 5% in supply voltage of an induction motor will change torque approximately -

  3. If a three phase squirrel cage induction motor runs slow, which of the following could not be the reason for that?

  4. What happens if load goes increasing of an Induction Motor?

  5. A three phase, 50 Hz, 6 pole induction motor runs at 960 rpm. The stator copper loss, core loss, and the rotational loss of the motor can be neglected. The percentage efficiency of the motor is
Need Expert Advice?
Test Series
RRB JE img
Railways
RRB JE (CBT 1 + CBT 2) 2026 Mock Test Series
1515 Tests 19 Tests Free
1848 Attempts
4.3(164)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App