A change of 5% in supply voltage of an induction motor will change torque approximately -
The torque developed by an induction motor is directly proportional to the square of the supply voltage. This is a fundamental relationship when analyzing induction motor performance.
Mathematically, this can be expressed as:
\( T \propto V^2 \)
Where:
Let's consider an initial condition with voltage \( V_1 \) and torque \( T_1 \). So, \( T_1 = k V_1^2 \) for some constant \( k \).
Now, suppose the supply voltage changes by 5%. Let the new voltage be \( V_2 \). If the voltage increases by 5%, then \( V_2 = V_1 + 0.05 V_1 = 1.05 V_1 \). If the voltage decreases by 5%, then \( V_2 = V_1 - 0.05 V_1 = 0.95 V_1 \). The question asks for the approximate change in torque, so we'll calculate the magnitude of the change.
The new torque \( T_2 \) will be proportional to the square of the new voltage \( V_2 \):
\( T_2 = k V_2^2 \)
Let's analyze the case where the voltage increases by 5%:
\( V_2 = 1.05 V_1 \)
So, the new torque is:
\( T_2 = k (1.05 V_1)^2 = k (1.05)^2 V_1^2 = k (1.1025) V_1^2 \)
Since \( T_1 = k V_1^2 \), we can write \( T_2 \) in terms of \( T_1 \):
\( T_2 = 1.1025 T_1 \)
The change in torque is \( T_2 - T_1 = 1.1025 T_1 - T_1 = 0.1025 T_1 \).
The percentage change in torque is \(\frac{\text{Change in Torque}}{\text{Original Torque}} \times 100\%\):
\( \text{Percentage Change} = \frac{0.1025 T_1}{T_1} \times 100\% = 0.1025 \times 100\% = 10.25\% \)
Now, let's analyze the case where the voltage decreases by 5%:
\( V_2 = 0.95 V_1 \)
So, the new torque is:
\( T_2 = k (0.95 V_1)^2 = k (0.95)^2 V_1^2 = k (0.9025) V_1^2 \)
Since \( T_1 = k V_1^2 \), we can write \( T_2 \) in terms of \( T_1 \):
\( T_2 = 0.9025 T_1 \)
The change in torque is \( T_2 - T_1 = 0.9025 T_1 - T_1 = -0.0975 T_1 \). The magnitude of the change is \( 0.0975 T_1 \).
The percentage change in torque is \(\frac{\text{Magnitude of Change}}{\text{Original Torque}} \times 100\%\):
\( \text{Percentage Change} = \frac{0.0975 T_1}{T_1} \times 100\% = 0.0975 \times 100\% = 9.75\% \)
Whether the supply voltage changes by +5% or -5%, the magnitude of the approximate percentage change in torque is very close to 10% (10.25% and 9.75% respectively). Therefore, a change of 5% in supply voltage of an induction motor will change torque approximately by 10%.