The problem asks for the cooling capacity required to freeze 1000 units of mixed fruit bars. This involves calculating the total heat removed during the cooling process and dividing it by the time taken, then converting the result to tons of refrigeration (TR).
Mass per bar = 100 g = 0.1 kg
Total mass ($m$) = Number of bars $\times$ Mass per bar
$ m = 1000 \times 0.1 \text{ kg} = 100 \text{ kg} $
The total heat removed ($Q$) is the sum of sensible heat removed above the freezing point, latent heat removed during freezing, and sensible heat removed below the freezing point.
Total Heat Removed ($Q$):
$ Q = Q_{\text{sensible, liquid}} + Q_{\text{latent}} + Q_{\text{sensible, solid}} $
$ Q = 25200 \text{ kJ} + 25000 \text{ kJ} + 3940 \text{ kJ} = 54140 \text{ kJ} $
Time taken ($\Delta t$) = 3 hours
Convert time to seconds: $ \Delta t = 3 \text{ hours} \times 3600 \text{ seconds/hour} = 10800 \text{ seconds} $
Cooling Rate ($\dot{Q}$) = Total Heat Removed / Time Taken
$ \dot{Q} = \frac{Q}{\Delta t} = \frac{54140 \text{ kJ}}{10800 \text{ s}} \approx 5.013 \text{ kJ/s} $
The conversion factor is approximately 1 TR = 3.517 kJ/s.
Cooling Capacity in TR = Cooling Rate / Conversion Factor
$ \text{Cooling Capacity (TR)} = \frac{5.013 \text{ kJ/s}}{3.517 \text{ kJ/s/TR}} \approx 1.425 \text{ TR} $
Rounding to two decimal places, the required cooling capacity is 1.43 TR.