Question

One thousand units of mixed fruit bar, each weighing 100 g with a surface area of 0.01 $m^2$, are frozen from 70 °C molten mass condition to -20 °C frozen storage condition within 3 hours. The specific heat capacity values of the bar are 3.6 kJ $kg^{-1}$ $K^{-1}$ and 1.97 kJ $kg^{-1}$ $K^{-1}$ before and after freezing point (0 °C) respectively. If the latent heat of crystallization is 250 kJ $kg^{-1}$, the cooling capacity of the refrigeration unit required in tons of refrigeration is

The correct answer is
1.43

Calculating Cooling Capacity for Freezing Mixed Fruit Bars

The problem asks for the cooling capacity required to freeze 1000 units of mixed fruit bars. This involves calculating the total heat removed during the cooling process and dividing it by the time taken, then converting the result to tons of refrigeration (TR).

1. Calculate Total Mass

Mass per bar = 100 g = 0.1 kg

Total mass ($m$) = Number of bars $\times$ Mass per bar

$ m = 1000 \times 0.1 \text{ kg} = 100 \text{ kg} $

2. Calculate Heat Removed

The total heat removed ($Q$) is the sum of sensible heat removed above the freezing point, latent heat removed during freezing, and sensible heat removed below the freezing point.

  • Sensible Heat (Liquid Phase): Heat removed while cooling from 70 °C to 0 °C. $ Q_{\text{sensible, liquid}} = m \times c_{p,l} \times (T_{\text{initial}} - T_{\text{freezing}}) $ $ Q_{\text{sensible, liquid}} = 100 \text{ kg} \times 3.6 \text{ kJ kg}^{-1} \text{ K}^{-1} \times (70 \text{ °C} - 0 \text{ °C}) $ $ Q_{\text{sensible, liquid}} = 100 \times 3.6 \times 70 = 25200 \text{ kJ} $
  • Latent Heat (Freezing): Heat removed at the freezing point (0 °C). $ Q_{\text{latent}} = m \times L_f $ $ Q_{\text{latent}} = 100 \text{ kg} \times 250 \text{ kJ kg}^{-1} $ $ Q_{\text{latent}} = 25000 \text{ kJ} $
  • Sensible Heat (Solid Phase): Heat removed while cooling from 0 °C to -20 °C. $ Q_{\text{sensible, solid}} = m \times c_{p,s} \times (T_{\text{freezing}} - T_{\text{final}}) $ $ Q_{\text{sensible, solid}} = 100 \text{ kg} \times 1.97 \text{ kJ kg}^{-1} \text{ K}^{-1} \times (0 \text{ °C} - (-20 \text{ °C})) $ $ Q_{\text{sensible, solid}} = 100 \times 1.97 \times 20 = 3940 \text{ kJ} $

Total Heat Removed ($Q$):

$ Q = Q_{\text{sensible, liquid}} + Q_{\text{latent}} + Q_{\text{sensible, solid}} $

$ Q = 25200 \text{ kJ} + 25000 \text{ kJ} + 3940 \text{ kJ} = 54140 \text{ kJ} $

3. Calculate Cooling Rate

Time taken ($\Delta t$) = 3 hours

Convert time to seconds: $ \Delta t = 3 \text{ hours} \times 3600 \text{ seconds/hour} = 10800 \text{ seconds} $

Cooling Rate ($\dot{Q}$) = Total Heat Removed / Time Taken

$ \dot{Q} = \frac{Q}{\Delta t} = \frac{54140 \text{ kJ}}{10800 \text{ s}} \approx 5.013 \text{ kJ/s} $

4. Convert to Tons of Refrigeration (TR)

The conversion factor is approximately 1 TR = 3.517 kJ/s.

Cooling Capacity in TR = Cooling Rate / Conversion Factor

$ \text{Cooling Capacity (TR)} = \frac{5.013 \text{ kJ/s}}{3.517 \text{ kJ/s/TR}} \approx 1.425 \text{ TR} $

Rounding to two decimal places, the required cooling capacity is 1.43 TR.

Was this answer helpful?

Important Questions from Refrigeration

  1. A refrigeration system based on reverse Carnot cycle operates between $-30\text{ }^\circ\text{C}$ and $20\text{ }^\circ\text{C}$. The refrigeration capacity of the system is $70\text{ kW}$. Heat rejected at the condenser to atmosphere (hot reservoir), in kW, is nearest to
  2. In a cascade refrigeration system, the COPs of the cooling cycle and cascade are 3.7 and 4.2, respectively. If tonnage (1 TR = 3.52 kW) of the cooling cycle is 15 and the cascade removes 70% of the total heat rejected in the liquid receiver of the cooling cycle, then the powers required by the cooling and cascade compressors in hp are ________ and ________, respectively.
  3. The horse power of the motor running the compressor of a refrigerator having COP of $4.5$ and extracting $200 \text{ kJ kg}^{-1}$ of evaporating heat with $1.5 \text{ kg min}^{-1}$ refrigerant flow rate is
  4. A cold storage takes 5 hours to bring down the temperature of 100 metric tons of potato from $35 \text{ °C}$ to $8 \text{ °C}$. The specific heat capacity of potato is $3.1 \text{ kJ kg}^{-1} \text{ °C}^{-1}$. The coefficient of performance (COP) and the latent heat of vapourisation of the refrigerant (R-22) at an evaporation temperature of $-10 \text{ °C}$ are 3.66 and $230 \text{ kJ kg}^{-1}$, respectively. Neglecting respiration heat load of potato, and assuming no power loss, the values of refrigerant flow rate and the power input to the compressor are
  5. A chiller working on mechanical vapour compression refrigeration system (COP = 4.5) is used for cooling 12500 kg of fresh cow milk ($c_p = 3.8$ kJ $kg^{-1}$ $K^{-1}$) from 30 °C to 4 °C in 3 hours. Assuming ideal compression process, the power consumed by the electric motor in kW and the tonnage of refrigeration (TR), respectively are
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App