What is the purpose of a Buchholz relay in transformer protection?

The correct answer is

To detect internal faults such as short circuits and arcing in oil

The purpose of a Buchholz relay in transformer protection can be explained through its function and operational context:

  1. Understanding Buchholz Relay: The Buchholz relay is a protective device used in oil-immersed transformers. It is placed between the main tank of the transformer and its conservator.
  2. Operation: It detects the presence of gas produced by internal faults such as short circuits and arcing within the transformer oil. When a fault occurs, the generated gas accumulates in the Buchholz relay, causing it to activate.
  3. Mechanism:
    • Minor faults generate small gas pockets, causing alarm signals.
    • More serious faults produce significant gas accumulation, tilting the float and triggering an electric contact to cut off the transformer from the circuit as a protection measure.
  4. Conclusion: From the given options, the correct answer is:

    To detect internal faults such as short circuits and arcing in oil

    . This correctly describes how a Buchholz relay is used in detecting internal transformer faults, helping to prevent damage by providing an early warning system.

Other options are incorrect because:

  • To detect overvoltage

    : This is typically handled by overvoltage relays or arrestors, not a Buchholz relay.
  • To measure core flux

    : Core flux is usually monitored by other means within a transformer's design, not by the Buchholz relay.
  • To measure temperature rise

    : Temperature is measured using thermometer-based devices or temperature sensors, not a Buchholz relay.
Was this answer helpful?

Similar Questions

  1. A limitation of Buchholz relay protection is:


Important Questions from Ratings of Circuit Breakers

  1. The highest rating of Triple pole with Neutral (TPN) MCB main switches available in the local market is _______.

  2. Which of the following fuses has the highest rating?

  3. A three - phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3s. The symmetrical breaking current is -

  4. A three-phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3 s. The symmetrical breaking current is

  5. In circuit breakers, which of the following methods is a NOT a correct method of increasing arc resistance?
Need Expert Advice?
Test Series
RRB JE img
Railways
RRB JE Prev. Yr. Paper (CBT 1 + CBT 2) Test Series
290 Tests 5 Tests Free
4475 Attempts
4.3(88)
English

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App