Find the making current for a circuit breaker rated at 1000 A, 3000 MVA, 66 kV, 3 sec, 3 – phase, oil circuit breaker

The correct answer is

66.92 kA

Understanding Circuit Breaker Making Current

The making current (also known as the peak making current) of a circuit breaker is the maximum asymmetrical current that the breaker can safely make (close) under short-circuit conditions. It's an important parameter for ensuring the breaker's mechanical and electrical integrity during the initial moments of a fault.

Calculating Rated Breaking Current

First, we need to calculate the RMS symmetrical breaking current ($I_b$) using the circuit breaker's rated breaking capacity ($S_{rated}$) and rated voltage ($V_{rated}$). The formula for a 3-phase system is:

$$I_b = \frac{S_{rated}}{\sqrt{3} \times V_{rated}}$$

Given:

  • Rated Breaking Capacity ($S_{rated}$) = 3000 MVA = $3000 \times 10^6$ VA
  • Rated Voltage ($V_{rated}$) = 66 kV = $66 \times 10^3$ V

Substitute the values into the formula:

$$I_b = \frac{3000 \times 10^6 \text{ VA}}{\sqrt{3} \times (66 \times 10^3) \text{ V}}$$

$$I_b = \frac{3000 \times 10^3}{\sqrt{3} \times 66} \text{ A}$$

$$I_b \approx \frac{3000000}{1.732 \times 66} \text{ A}$$

$$I_b \approx \frac{3000000}{114.312} \text{ A}$$

$$I_b \approx 26243.7 \text{ A}$$

Converting this to kiloamperes (kA):

$$I_b \approx 26.24 \text{ kA}$$

Calculating Making Current

The making current ($I_m$) is typically calculated as a multiple of the RMS symmetrical breaking current. This multiple, known as the making current factor (K), accounts for the DC offset that occurs during a short circuit. For standard industrial applications, a common factor is K = 2.55 (based on IEC standards for a typical X/R ratio).

The formula is:

$$I_m = K \times I_b$$

Using the calculated breaking current and the factor K = 2.55:

$$I_m = 2.55 \times 26.2437 \text{ kA}$$

$$I_m \approx 66.921 \text{ kA}$$

Final Result

Therefore, the making current for the circuit breaker is approximately 66.92 kA.

Was this answer helpful?

Important Questions from Ratings of Circuit Breakers

  1. The highest rating of Triple pole with Neutral (TPN) MCB main switches available in the local market is _______.

  2. Which of the following fuses has the highest rating?

  3. A three - phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3s. The symmetrical breaking current is -

  4. A three-phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3 s. The symmetrical breaking current is

  5. In circuit breakers, which of the following methods is a NOT a correct method of increasing arc resistance?
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App