A three-phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3 s. The symmetrical breaking current is

The correct answer is

35 kA

Circuit Breaker Symmetrical Breaking Current Explained

This solution explains how to calculate the symmetrical breaking current for a three-phase oil circuit breaker using the provided ratings.

Parameters Provided

The question provides the following details about the oil circuit breaker:

  • Type: Three-phase oil circuit breaker
  • System Voltage: 33 kV (This is the line-to-line voltage, $V_L$)
  • Rated Current: 1200 A (This is the continuous current rating)
  • Rated Capacity: 2000 MVA (This is the three-phase breaking capacity, $S$)
  • Rated Time: 3 s (This typically refers to the circuit breaker's interrupting time rating)

Formula for Symmetrical Breaking Current

The symmetrical breaking current ($I_b$) is the RMS value of the AC component of the current during the interruption process. It is calculated using the three-phase breaking capacity ($S$) and the line-to-line voltage ($V_L$) of the system. The formula is:

$$ I_b = \frac{S}{\sqrt{3} \times V_L} $$

Where:

  • $I_b$ is the symmetrical breaking current in kiloamperes (kA).
  • $S$ is the three-phase breaking capacity in megavolt-amperes (MVA).
  • $V_L$ is the line-to-line voltage in kilovolts (kV).
  • $\sqrt{3}$ represents the factor for three-phase power calculations.

Calculation Steps

Let's use the given values in the formula:

  1. Substitute Values: Plug the given MVA rating and voltage into the formula.
    • $S = 2000$ MVA
    • $V_L = 33$ kV

    $$ I_b = \frac{2000 \text{ MVA}}{\sqrt{3} \times 33 \text{ kV}} $$

  2. Calculate the Denominator: First, calculate the product of $\sqrt{3}$ and the voltage.

    $$ \sqrt{3} \times 33 \approx 1.732 \times 33 \approx 57.156 $$

  3. Divide Capacity by Denominator: Now, divide the MVA rating by the result from the previous step.

    $$ I_b = \frac{2000}{57.156} \text{ kA} $$

  4. Final Result: Perform the division to find the breaking current.

    $$ I_b \approx 35.00 \text{ kA} $$

Result and Option Matching

The calculated symmetrical breaking current is approximately 35 kA. Comparing this result with the given options:

  • 1200 A (Incorrect - This is the rated current)
  • 3600 A (Incorrect)
  • 35 kA (Correct)
  • 104.8 kA (Incorrect)

Therefore, the symmetrical breaking current for the specified oil circuit breaker is 35 kA.

Was this answer helpful?

Important Questions from Ratings of Circuit Breakers

  1. The highest rating of Triple pole with Neutral (TPN) MCB main switches available in the local market is _______.

  2. Which of the following fuses has the highest rating?

  3. A three - phase, 33 kV oil circuit breaker is rated 1200 A, 2000 MVA, 3s. The symmetrical breaking current is -

  4. In circuit breakers, which of the following methods is a NOT a correct method of increasing arc resistance?
  5. A three-phase 33 kV, oil-circuit breaker is rated 1500 A, 2000 MVA, 2 s. The symmetrical breaking current for this breaker would be

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App