The current on a high voltage line is measured using:

This question was previously asked in
RRB ALP 2018 CBT 2 Fitter Question Paper (21-Jan-2019) (Shift 3)
The correct answer is

Current transformer

Understanding High Voltage Current Measurement

Measuring current on a high voltage line presents significant challenges due to the high magnitude of the current and, more importantly, the extremely high voltage present. Direct measurement methods are often unsafe for personnel and can introduce undesirable impedance into the high voltage system.

The Role of Current Transformers (CTs)

A current transformer (CT) is a type of transformer specifically designed to measure alternating current (AC). It produces a reduced current proportional to the current in the high voltage line, allowing standard meters and relays to be used safely.

Here's how a current transformer works in the context of high voltage lines:

  • The high voltage line passes through or around the core of the current transformer, effectively acting as the primary winding (often just a single turn).
  • A secondary winding with many turns is connected to a low-current measuring instrument (like an ammeter) or a protective relay.
  • The current in the high voltage primary induces a proportional current in the secondary winding, stepped down by the turns ratio of the transformer.
  • Crucially, the current transformer provides electrical isolation between the high voltage circuit and the low-voltage measuring circuit, ensuring the safety of the operators and equipment connected to the secondary.

This isolation and current stepping-down capability make the current transformer the standard device for measuring current on high voltage lines.

Why Other Options Are Not Suitable for High Voltage Current Measurement

Let's consider why the other options are not typically used for measuring current directly on high voltage transmission lines:

  • Current shunt: A current shunt is a low-value precision resistor placed in series with the circuit. Measuring current involves measuring the voltage drop across the shunt. While effective for lower voltages and currents, using a shunt on a high voltage line would expose the measurement circuit to the full high voltage and would require a very robust, high-power resistor capable of handling the significant power dissipation (\(P = I^2R\)) at high currents, making it impractical and unsafe.
  • Voltage transformer: A voltage transformer (also known as a potential transformer or PT) is used to step down high voltages to lower, measurable levels for voltmeters or relays. It measures voltage, not current.
  • Load resistor: A load resistor is a component used to dissipate power or terminate a circuit. It is not a standard measuring device for current, especially not in the context of high voltage lines where it would significantly impact the circuit operation and safety.

Therefore, the current transformer is the appropriate and safe instrument for measuring current on high voltage lines.

Conclusion on High Voltage Current Measurement Device

Based on the analysis of how different measurement devices work and the unique challenges of measuring current on high voltage lines, the current transformer is the universally accepted solution due to its ability to step down current safely and provide electrical isolation.

Comparison of Measurement Devices for High Voltage Lines
Device Purpose Suitable for High Voltage Current Measurement? Reason
Current Transformer (CT) Measure current Yes Steps down current, provides isolation.
Current Shunt Measure current (via voltage drop) No Exposes measurement circuit to high voltage, impractical power dissipation.
Voltage Transformer (VT/PT) Measure voltage No Measures voltage, not current.
Load Resistor Dissipate power/terminate No Not a standard measurement device, impacts circuit operation.

Revision Table: Electrical Measurement Devices

Key Electrical Measurement Components
Component Primary Function Typical Application
Current Transformer (CT) Current stepping down and isolation Measuring high AC currents in power systems
Voltage Transformer (VT/PT) Voltage stepping down and isolation Measuring high AC voltages in power systems
Current Shunt Creating proportional voltage drop from current Measuring DC or AC currents, typically at lower voltages/currents
Resistor Introduce resistance, limit current, dissipate heat Wide range of applications, not a primary current measurement device for lines

Additional Information on Current Transformers and High Voltage Systems

Current transformers are critical components in electrical power systems, serving not only for measurement but also for protection. Relays connected to the secondary of a CT can detect overload or fault conditions based on excessive current and trigger protective actions like opening circuit breakers.

There are different types of current transformers depending on the application and voltage level, including:

  • Window CTs: The conductor passes through a "window" in the CT core.
  • Bar-type CTs: Have a built-in primary bar as part of the CT.
  • Bushing CTs: Installed around the bushings of transformers or circuit breakers.
  • Wound CTs: Have a primary winding within the transformer body, used for lower currents or testing.

Proper grounding of the CT secondary circuit is essential for safety to prevent high voltages from appearing on the low-voltage side in case of insulation failure.

Was this answer helpful?

Similar Questions

  1. Steel poles are painted to prevent them from:

  2. What is the purpose of a lighting arrester connected between the line and earth in a power S/M?

  3. Domestic customers are provided with single phase supply voltage of

  4. From the given options, identify the type of lug used for connecting an aluminum cable to a copper bus bar.

  5. In which of the following regions of a cable, voltage stress is maximum?

  6. What is the color of neutral in three core flexible cables?

  7. The current carrying capacity of cables is:

  8. The SMPS is used to transform power from AC or DC to:

  9. Which among the below is not generally used for distribution systems?

  10. The protective equipment used to protect equipment against lightning stroke is:


Important Questions from Transmission and Distribution

  1. The capacitance and inductance per unit length of a three-phase line, operating at 110 kV are 0.01 μF and 2.5 mH. The surge impedance of the line is:

  2. Which of the following statements about the EHV lines is INCORRECT?

  3. Now-a-days, aluminium wires are more widely used than copper because

  4. The factor on which earth resistance value depends on

  5. Steel poles are painted to prevent them from:

Need Expert Advice?
Upcoming Exams
RRB Technician
October 06, 2026
RRB JE
October 27, 2026
RRB ALP
November 03, 2026
Test Series
RRB ALP img
Railways
RRB ALP 2026 Mock Test series
1035 Tests 1 Tests Free
1088 Attempts
4.3(239)
English, Hindi

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App