The capacitance and inductance per unit length of a three-phase line, operating at 110 kV are 0.01 μF and 2.5 mH. The surge impedance of the line is:
500 Ω
The surge impedance of a transmission line is a characteristic impedance that represents the ratio of the voltage wave to the current wave propagating along the line. It is determined by the physical properties of the line, specifically its inductance and capacitance per unit length.
The surge impedance ($\text{Z}_\text{s}$) of a transmission line can be calculated using the inductance per unit length ($\text{L}$) and the capacitance per unit length ($\text{C}$) with the following formula:
$$ \text{Z}_\text{s} = \sqrt{\frac{\text{L}}{\text{C}}} $$
From the question, we are given the following values for the three-phase line:
To use these values in the formula, we need to convert them to standard units (Farads and Henrys):
Now, substitute the converted values into the surge impedance formula:
$$ \text{Z}_\text{s} = \sqrt{\frac{\text{L}}{\text{C}}} $$
$$ \text{Z}_\text{s} = \sqrt{\frac{2.5 \times 10^{-3} \text{ H}}{1 \times 10^{-8} \text{ F}}} $$
$$ \text{Z}_\text{s} = \sqrt{2.5 \times 10^{-3} \times 10^{8}} \text{ } \Omega $$
$$ \text{Z}_\text{s} = \sqrt{2.5 \times 10^{5}} \text{ } \Omega $$
$$ \text{Z}_\text{s} = \sqrt{25 \times 10^{4}} \text{ } \Omega $$
$$ \text{Z}_\text{s} = \sqrt{25} \times \sqrt{10^{4}} \text{ } \Omega $$
$$ \text{Z}_\text{s} = 5 \times 10^{2} \text{ } \Omega $$
$$ \text{Z}_\text{s} = 500 \text{ } \Omega $$
The calculated surge impedance of the transmission line is 500 $\Omega$.