The question asks which transformer type requires its secondary winding to be always kept closed.
The secondary winding of a CT must always be connected to a closed circuit (a burden, like an ammeter or relay coil, or simply short-circuited) for the following reasons:
Based on its operational principle and safety requirements, the Current transformer is the type where the secondary winding must always be kept closed.
Connection of voltage transformer and current transformer across line are respectively.
A 100 : 5 current transformer is used in conjunction with a 5 A ammeter. If the later reads 3.5 A, find the line current.
Up to a voltage of __________, Potential Transformers (PTs) are usually of dry type.
A potential transformer of 12000/112 V and current transformer of 80/6 A are used to measure voltage and current in a transmission line. If the voltmeter indicates 120 V and current reads 5 A, what is the voltage and current in this line?
The table lists two instrument transformers and their features:
| Instrument Transformers | Features |
| P) Primary is connected in parallel to the grid | |
| X) Current Transformer (CT) | Q) Open circuited secondary is not desirable |
| Y) Potential Transformer (PT) | R) Primary current is the line current |
| S) Secondary burden affects the primary current |
The correct matching of the two columns is
In which of the following transformers, is the secondary winding always kept closed?