Which of the following options is true with respect to extending the range of a wattmeter using instrument transformers?

The correct answer is

The secondary winding of current transformer is connected in series with the current coil of wattmeter and ammeter.

Understanding Wattmeter Range Extension with Instrument Transformers

Extending the range of a wattmeter, which measures electrical power, is often necessary when dealing with high voltages or currents that exceed the instrument's direct measurement capability. This is typically achieved using instrument transformers: Current Transformers (CTs) and Potential Transformers (PTs).

Instrument transformers provide isolation between the high-voltage/high-current circuit and the measuring instruments, and they also step down the voltage and current to levels safe and suitable for the instruments. The wattmeter has two coils: a current coil (connected in series with the load circuit or a CT secondary) and a pressure or voltage coil (connected across the load circuit or a PT secondary).

Connecting Instrument Transformers to a Wattmeter

The connection of instrument transformers to a wattmeter is crucial for correct power measurement and range extension:

  • Current Transformer (CT): The primary winding of the CT is connected in series with the load circuit, carrying the main load current. The secondary winding of the CT produces a scaled-down current proportional to the primary current. This secondary winding is connected in series with the current coil of the wattmeter (and any series-connected ammeter).
  • Potential Transformer (PT): The primary winding of the PT is connected in parallel across the load circuit (or across the line), experiencing the main load voltage. The secondary winding of the PT produces a scaled-down voltage proportional to the primary voltage. This secondary winding is connected in parallel across the pressure coil of the wattmeter (and any parallel-connected voltmeter).

Analyzing the Options for Wattmeter Range Extension

Let's evaluate each given option based on the standard connections for extending a wattmeter's range using CTs and PTs:

  1. The primary winding of potential transformer is connected in series with the load.

    This statement is incorrect. The primary winding of a potential transformer is connected in parallel across the line or load to measure the voltage.

  2. The secondary winding of potential transformer is connected in series with the pressure coil of wattmeter and voltmeter.

    This statement is incorrect. The secondary winding of a potential transformer is connected in parallel across the pressure coil of the wattmeter and any voltmeter. They are connected to the same voltage from the PT secondary.

  3. The secondary winding of current transformer is connected in series with the current coil of wattmeter and ammeter.

    This statement is correct. The secondary winding of a current transformer supplies a current that is proportional to the load current. This scaled-down current needs to flow through the current-sensing elements, which are the current coil of the wattmeter and the ammeter. Connecting them in series ensures that the CT secondary current passes through both instruments.

  4. The primary winding of current transformer is connected in parallel with the load.

    This statement is incorrect. The primary winding of a current transformer is connected in series with the load so that it carries the full load current.

Based on the correct principles of connecting instrument transformers for wattmeter range extension, the statement regarding the secondary winding of the current transformer being connected in series with the wattmeter's current coil and an ammeter is the accurate description.

Was this answer helpful?

Important Questions from Instrument Transformers

  1. In which of the following transformers, is the secondary winding always kept closed?

  2. Instrument transformers are used in which type of circuits?

  3. What is the use of potential transformer?

  4. A 100 : 5 current transformer is used in conjunction with a 5 A ammeter. If the later reads 3.5 A, find the line current.

  5. Up to a voltage of __________, Potential Transformers (PTs) are usually of dry type.