All Exams Test series for 1 year @ ₹349 only
Question

View factor of a large cylinder of 10 cm in radius and 60 cm in length from a coaxial smaller cylinder of 5 cm radius and the same length is 0.34. View factor of the larger cylinder of itself (concave inner surface) is 0.25. The view factor of the larger cylinder with respect to either annular end is

The correct answer is
0.29

View Factor Calculation for Coaxial Cylinders

This solution details the calculation of the view factor for a coaxial cylinder configuration using fundamental radiation heat transfer principles.

Given Information

  • Large cylinder radius: $r_1 = 10$ cm
  • Small cylinder radius: $r_2 = 5$ cm
  • Cylinder length: $L = 60$ cm (common length)
  • View factor from the small cylinder surface ($A_2$) to the large cylinder surface ($A_1$): $F_{2 \to 1} = 0.34$
  • View factor of the large cylinder's inner surface ($A_1$) to itself: $F_{1 \to 1} = 0.25$

Objective: Calculate the view factor from the large cylinder's inner surface ($A_1$) to either annular end ($A_E$). Let this be $F_{1 \to E}$.

Applying View Factor Rules

Consider the surfaces involved:

  • Surface 1 ($A_1$): The inner cylindrical surface of the larger cylinder. Area $A_1 = 2 \pi r_1 L$.
  • Surface 2 ($A_2$): The inner cylindrical surface of the smaller cylinder. Area $A_2 = 2 \pi r_2 L$.
  • Surface E ($A_E$): The two identical annular end surfaces of the larger cylinder.

Two key view factor rules are applied:

  1. Summation Rule: The total view factor from a surface to all other surfaces must equal 1. For Surface 1: $F_{1 \to 1} + F_{1 \to 2} + F_{1 \to E} + F_{1 \to E} = 1$ Since there are two identical annular ends, the rule becomes: $F_{1 \to 1} + F_{1 \to 2} + 2 F_{1 \to E} = 1$
  2. Reciprocity Rule: The view factor between two surfaces is related by their areas: $A_1 F_{1 \to 2} = A_2 F_{2 \to 1}$

Calculations

Step 1: Calculate $F_{1 \to 2}$ using the reciprocity rule.

Substitute the area formulas into the reciprocity rule:

$(2 \pi r_1 L) F_{1 \to 2} = (2 \pi r_2 L) F_{2 \to 1}$

The $2 \pi L$ terms cancel out, simplifying to:

$r_1 F_{1 \to 2} = r_2 F_{2 \to 1}$

Plug in the given values:

$(10 \text{ cm}) F_{1 \to 2} = (5 \text{ cm}) (0.34)$ $10 F_{1 \to 2} = 1.7$ $F_{1 \to 2} = \frac{1.7}{10} = 0.17$

Step 2: Calculate $F_{1 \to E}$ using the summation rule.

Substitute the known values ($F_{1 \to 1} = 0.25$ and the calculated $F_{1 \to 2} = 0.17$) into the summation equation:

$0.25 + 0.17 + 2 F_{1 \to E} = 1$ $0.42 + 2 F_{1 \to E} = 1$

Solve for $F_{1 \to E}$:

$2 F_{1 \to E} = 1 - 0.42$ $2 F_{1 \to E} = 0.58$ $F_{1 \to E} = \frac{0.58}{2}$ $F_{1 \to E} = 0.29$

The view factor of the larger cylinder with respect to either annular end is 0.29.

Was this answer helpful?

Important Questions from Radiation

  1. A body is placed inside a perfectly black enclosure and is allowed to reach thermal equilibrium. According to the Kirchhoff’s identity, which one of the following is equal to the emissivity of the body at a given wavelength?
  2. Thermal radiation takes place at a surface which has reflectivity of 0.55 and a transmissivity of 0.032. What is the value of absorptivity?

  3. Two infinitely large parallel plates (I and II) are held at temperatures $T_I$ and $T_{II}$ ($T_I > T_{II}$) respectively, and placed at a distance $2d$ apart in vacuum. An infinitely large flat radiation shield (III) is placed in parallel in between I and II. The emissivities of all the plates are equal. The ratio of the steady state radiative heat fluxes with and without the shield is:

  4. Two very large parallel walls (gray bodies) facing each other have emissivities of 0.5 and 0.7. The view factor between these two walls is ________.
  5. The space between two hollow concentric spheres of radii 0.1 m and 0.2 m is under vacuum.
    Exchange of radiation (uniform in all directions) occurs only between the outer surface ($S_1$) of the smaller sphere and the inner surface ($S_2$) of the larger sphere. The fraction (rounded off to the second decimal place) of the radiation energy leaving $S_2$, which reaches $S_1$ is
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App