The power taken by a 3-ϕ load is given by the expression

The correct answer is

√3 VLIL cos ϕ

Understanding 3-Phase Load Power

In electrical engineering, understanding the power consumed by a 3-phase load is crucial. A 3-phase system involves three alternating currents that are out of phase with each other. The power consumed by such a load depends on the voltage, current, and the phase difference between them.

Formula for 3-Phase Power

The total active power (P) consumed by a balanced 3-phase load can be calculated using the line voltage ($V_L$), the line current ($I_L$), and the power factor ($\cos \varphi$). The power factor represents the cosine of the angle ($\varphi$) between the voltage and current phasors.

The standard formula for the active power in a 3-phase system, when using line voltage and line current, is:

$$P = \sqrt{3} \times V_L \times I_L \times \cos \varphi$$

Where:

  • $P$ is the active power in Watts (W).
  • $V_L$ is the Line-to-Line voltage in Volts (V).
  • $I_L$ is the Line current in Amperes (A).
  • $\cos \varphi$ is the power factor of the load.

Analyzing the Options

Let's examine the given options in light of the correct formula:

  • Option 1:

    3 $V_L$$I_L$ $\cos \varphi$

    - This formula is typically associated with the sum of powers in a single-phase system or relates differently to line/phase quantities in 3-phase systems depending on context, but it's not the standard expression for total 3-phase power using line values.
  • Option 2:

    $\sqrt{3}$ $V_L$$I_L$ $\cos \varphi$

    - This matches the standard formula for calculating the total active power in a balanced 3-phase load using line voltage and line current.
  • Option 3:

    3 $V_L$$I_L$ $\sin \varphi$

    - This uses the sine of the angle instead of the cosine, which is incorrect for active power calculation.
  • Option 4:

    $\sqrt{3}$ $V_L$$I_L$ $\sin \varphi$

    - This uses the sine term, making it incorrect for active power.

Therefore, the correct expression for the power taken by a 3-phase load using line voltage ($V_L$) and line current ($I_L$) is $\sqrt{3} V_L I_L \cos \varphi$.

Was this answer helpful?

Important Questions from Three Phase Circuits

  1. In a balanced three-phase, star-connected system, the phase difference between phase voltages and their respective line voltages is:

  2. Three equal impedances are first connected in star across a balanced 3 phase supply. If connected in delta across the same supply

  3. A three phase circuit is connected with balanced delta connected load of impedance 100 Ω. If the current in each phase is 5 A, the voltage across each load will be

  4. A load of three impedances each (6 + j9) is supplied through a line having an impedance of (1 + j2) Ω. The supply voltage is 400 V at 50 Hz. Determine input and output powers respectively when the load is star connected.

  5. Which is correct for single phase supply comparison to three phase supply?
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App