A load of three impedances each (6 + j9) is supplied through a line having an impedance of (1 + j2) Ω. The supply voltage is 400 V at 50 Hz. Determine input and output powers respectively when the load is star connected.
6591 W and 5649 W
The question asks us to calculate the input power and output power for a three-phase load that is connected in a star configuration. We are given the impedance of each load element ($Z_L$), the impedance of the supply line per phase ($Z_{line}$), and the supply voltage ($V_S$).
For a star connection, the phase voltage is the line voltage divided by $\sqrt{3}$.
$$ V_{ph} = \frac{V_{line}}{\sqrt{3}} = \frac{400 \text{ V}}{\sqrt{3}} \approx 230.94 \text{ V} $$The total impedance experienced by each phase is the sum of the line impedance and the load impedance, as they are in series for each phase.
$$ Z_{total} = Z_{line} + Z_L = (1 + j2) \text{ Ω} + (6 + j9) \text{ Ω} = (1+6) + j(2+9) \text{ Ω} $$ $$ Z_{total} = (7 + j11) \text{ Ω} $$The resistance component of the total impedance is $R_{total} = 7$ Ω, and the reactance component is $X_{total} = 11$ Ω.
The phase current is determined by the phase voltage and the total phase impedance.
$$ |I_{ph}| = \frac{|V_{ph}|}{|Z_{total}|} $$First, find the magnitude of the total impedance:
$$ |Z_{total}| = \sqrt{R_{total}^2 + X_{total}^2} = \sqrt{7^2 + 11^2} = \sqrt{49 + 121} = \sqrt{170} \approx 13.04 \text{ Ω} $$Now, calculate the phase current magnitude:
$$ |I_{ph}| = \frac{230.94 \text{ V}}{13.04 \text{ Ω}} \approx 17.71 \text{ A} $$We need the square of the current magnitude for power calculations:
$$ |I_{ph}|^2 \approx (17.71)^2 \approx 313.64 \text{ A}^2 $$Using more precise values: $|I_{ph}|^2 = (\frac{400}{\sqrt{3}\sqrt{170}})^2 = \frac{160000}{3 \times 170} = \frac{160000}{510} \approx 313.7255$
The output power is the power dissipated in the load resistance ($R_L$).
The resistance of the load per phase is $R_L = 6$ Ω.
$$ P_{out} = 3 \times |I_{ph}|^2 \times R_L $$ $$ P_{out} = 3 \times \left(\frac{160000}{510}\right) \times 6 \text{ W} $$ $$ P_{out} = \frac{3 \times 160000 \times 6}{510} \text{ W} = \frac{2880000}{510} \text{ W} \approx 5647.06 \text{ W} $$This value is approximately 5649 W.
The input power is the total power dissipated in both the line resistance ($R_{line}$) and the load resistance ($R_L$).
The resistance of the line per phase is $R_{line} = 1$ Ω.
The total resistance per phase is $R_{total} = R_{line} + R_L = 1 + 6 = 7$ Ω.
$$ P_{in} = 3 \times |I_{ph}|^2 \times R_{total} $$ $$ P_{in} = 3 \times \left(\frac{160000}{510}\right) \times 7 \text{ W} $$ $$ P_{in} = \frac{3 \times 160000 \times 7}{510} \text{ W} = \frac{3360000}{510} \text{ W} \approx 6588.24 \text{ W} $$This value is approximately 6591 W.
The calculated input power is approximately 6591 W, and the output power is approximately 5649 W.
Therefore, the input and output powers are 6591 W and 5649 W, respectively.
In a balanced three-phase, star-connected system, the phase difference between phase voltages and their respective line voltages is:
Three equal impedances are first connected in star across a balanced 3 phase supply. If connected in delta across the same supply
The power taken by a 3-ϕ load is given by the expression
A three phase circuit is connected with balanced delta connected load of impedance 100 Ω. If the current in each phase is 5 A, the voltage across each load will be