All Exams Test series for 1 year @ ₹349 only
Question

Three equal impedances are first connected in star across a balanced 3 phase supply. If connected in delta across the same supply

The correct answer is

Power consumed will increase three-fold

Star vs Delta Connection: Impedance and Power Analysis

This question explores the behavior of three equal impedances when connected first in a star configuration and then in a delta configuration across the same balanced 3-phase supply. We need to understand how this change affects the phase current, line current, and overall power consumption.

Understanding Star and Delta Connections

In a 3-phase system:

  • Star (Y) Connection: Has a common neutral point. The line voltage ($V_L$) is $\sqrt{3}$ times the phase voltage ($V_{ph}$), and the line current ($I_L$) is equal to the phase current ($I_{ph}$).
    • $V_{ph} = \frac{V_L}{\sqrt{3}}$
    • $I_L = I_{ph}$
  • Delta ($\Delta$) Connection: Forms a closed loop. The line voltage ($V_L$) is equal to the phase voltage ($V_{ph}$), and the line current ($I_L$) is $\sqrt{3}$ times the phase current ($I_{ph}$).
    • $V_{ph} = V_L$
    • $I_L = \sqrt{3} \times I_{ph}$

Analyzing the Impedance Changes

Let the impedance per phase be denoted by $Z$. Since the three impedances are equal:

Star Connection Calculations

When the three equal impedances ($Z$) are connected in star:

  • Phase Voltage: $V_{ph(star)} = \frac{V_L}{\sqrt{3}}$
  • Phase Current: $I_{ph(star)} = \frac{V_{ph(star)}}{Z} = \frac{V_L}{\sqrt{3}Z}$
  • Line Current: $I_{L(star)} = I_{ph(star)} = \frac{V_L}{\sqrt{3}Z}$

Delta Connection Calculations

When the same three equal impedances ($Z$) are connected in delta across the same supply:

  • Phase Voltage: $V_{ph(delta)} = V_L$
  • Phase Current: $I_{ph(delta)} = \frac{V_{ph(delta)}}{Z} = \frac{V_L}{Z}$
  • Line Current: $I_{L(delta)} = \sqrt{3} \times I_{ph(delta)} = \sqrt{3} \times \frac{V_L}{Z}$

Comparing Currents and Power

Phase Current Comparison

Comparing the phase currents:

Ratio: $\frac{I_{ph(delta)}}{I_{ph(star)}} = \frac{V_L/Z}{V_L/(\sqrt{3}Z)} = \sqrt{3}$

The phase current in the delta connection is $\sqrt{3}$ times the phase current in the star connection. This means the phase current increases, but not necessarily tripled or doubled as stated in options 1 and 2.

Line Current Comparison

Comparing the line currents:

Ratio: $\frac{I_{L(delta)}}{I_{L(star)}} = \frac{\sqrt{3} V_L/Z}{V_L/(\sqrt{3}Z)} = \sqrt{3} \times \sqrt{3} = 3$

The line current in the delta connection is three times the line current in the star connection. Option 3 is therefore incorrect.

Power Consumption Comparison

The power consumed by an impedance $Z$ with resistance $R$ and current $I$ is $P = 3 \times I_{ph}^2 \times R$. Alternatively, using line current, $P = 3 \times I_L^2 \times |Z| \times \cos(\phi)$, where $\cos(\phi)$ is the power factor.

Let's compare using phase currents:

  • Power in Star: $P_{star} = 3 \times (I_{ph(star)})^2 \times R = 3 \times \left(\frac{V_L}{\sqrt{3}Z}\right)^2 \times R$
  • Power in Delta: $P_{delta} = 3 \times (I_{ph(delta)})^2 \times R = 3 \times \left(\frac{V_L}{Z}\right)^2 \times R$

Comparing the power:

Ratio: $\frac{P_{delta}}{P_{star}} = \frac{3 \times (V_L/Z)^2 \times R}{3 \times (V_L/(\sqrt{3}Z))^2 \times R} = \frac{(V_L/Z)^2}{(V_L/(\sqrt{3}Z))^2} = \frac{V_L^2/Z^2}{V_L^2/(3Z^2)} = 3$

The power consumed in the delta connection is three times the power consumed in the star connection.

Conclusion

Based on the analysis, when three equal impedances are switched from a star connection to a delta connection across the same balanced 3-phase supply:

  • Phase current increases by a factor of $\sqrt{3}$.
  • Line current triples (increases by a factor of 3).
  • Power consumed increases three-fold (increases by a factor of 3).

Therefore, the statement 'Power consumed will increase three-fold' is correct.

Was this answer helpful?

Important Questions from Three Phase Circuits

  1. In a balanced three-phase, star-connected system, the phase difference between phase voltages and their respective line voltages is:

  2. The power taken by a 3-ϕ load is given by the expression

  3. A three phase circuit is connected with balanced delta connected load of impedance 100 Ω. If the current in each phase is 5 A, the voltage across each load will be

  4. A load of three impedances each (6 + j9) is supplied through a line having an impedance of (1 + j2) Ω. The supply voltage is 400 V at 50 Hz. Determine input and output powers respectively when the load is star connected.

  5. Which is correct for single phase supply comparison to three phase supply?
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App