Question

Milk enters at $25$ $^\circ C$ through inner pipe of a concentric double pipe heat exchanger. Hot water enters at $82.5$ $^\circ C$ and flows countercurrently (flow rate = $1.2$ kg.s$^{-1}$) through the annular region. The diameter of inner pipe, length of the pipe and average overall heat transfer coefficient are $60$ mm, $6$ m, and $2100$ W.m$^{-2}$.K$^{-1}$, respectively. The average values of specific heat capacity of water and milk are $4.18$ kJ.kg$^{-1}$.K$^{-1}$ and $3.95$ kJ.kg$^{-1}$.K$^{-1}$, respectively. The effectiveness of the heat exchanger is $0.572$ and the NTU is $1.01$. Assuming the steady-state condition and considering $\pi$ as $3.14$, the temperature of hot water at exit of the pipe is __________ $^\circ C$. (Rounded off to 1 decimal place)

Given Data

Inlet Temperature of Hot Water (Thi) = 82.5 °C
Inlet Temperature of Milk (Tci) = 25 °C
Mass flow rate of hot water (mh) = 1.2 kg/s
Specific Heat of Water (cph) = 4.18 kJ/kg.K = 4180 J/kg.K
Diameter (D) = 60 mm = 0.06 m
Length (L) = 6 m
Overall Heat Transfer Coefficient (U) = 2100 W/m².K
Effectiveness (ε) = 0.572
NTU = 1.01
π = 3.14

Step 1: Calculate Heat Transfer Area (A)

A = π × D × L
A = 3.14 × 0.06 × 6
A = 1.1304 m²

Step 2: Calculate Overall Heat Conductance (UA)

UA = U × A
UA = 2100 × 1.1304
UA = 2373.84 W/K

Step 3: Calculate Minimum Heat Capacity Rate (Cmin)

Using the NTU definition: NTU = UA / Cmin
1.01 = 2373.84 / Cmin
Cmin = 2373.84 / 1.01
Cmin = 2350.34 W/K

Step 4: Calculate Hot Fluid Heat Capacity Rate (Ch)

Ch = mh × cph
Ch = 1.2 × 4180
Ch = 5016 W/K

Step 5: Calculate Maximum Heat Transfer (Qmax)

Qmax = Cmin × (Thi - Tci)
Qmax = 2350.34 × (82.5 - 25)
Qmax = 2350.34 × 57.5
Qmax = 135,144.55 W

Step 6: Calculate Actual Heat Transfer (Q)

Q = ε × Qmax
Q = 0.572 × 135,144.55
Q = 77,302.68 W

Step 7: Calculate Exit Temperature of Hot Water (Tho)

Using the energy balance equation for hot water:
Q = Ch × (Thi - Tho)
77,302.68 = 5016 × (82.5 - Tho)
82.5 - Tho = 77,302.68 / 5016
82.5 - Tho = 15.41
Tho = 82.5 - 15.41
Tho = 67.09 °C

Final Answer

Rounded to 1 decimal place:
67.1 °C

Was this answer helpful?

Important Questions from Heat Exchangers

  1. In a counter-current flow double pipe heat exchanger (DPHE), temperature difference between the hot and cold liquids at all positions is held constant at C. If the effectiveness of the heat exchanger is 0.65 and heat capacity ratio of hot and cold liquids is 1, the number of transfer units (NTU) is ________.
  2. Milk enters into the heating section of a high temperature short time (HTST) pasteurization plant at a temperature of $45^\circ C$ and leaves at $72^\circ C$. Hot water at temperature of $95 \text{ }^\circ C$ enters counter- currently into the heat exchanger and leaves at $77^\circ C$. The effectiveness of the heat exchanger is
  3. The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________

  4. Hot refined oil at $120 \text{ °C}$ enters a concentric tube-in-tube heat exchanger (HE) at the rate of $20 \text{ kg min}^{-1}$. The oil is cooled by water entering at a temperature of $30 \text{ °C}$ from the other end of the HE at the rate of $50 \text{ kg min}^{-1}$. Specific heat capacities of oil and water are $1.9$ and $4.2 \text{ kJ kg}^{-1} \text{ °C}^{-1}$, respectively. The effectiveness of the HE may be taken as $0.7$. Assuming no heat loss to the surrounding under steady-state condition, the exit temperature of water from the HE in $ \text{°C}$ is
  5. Fruit juice entering at 30 °C is being pasteurized in a double pipe counter flow heat exchanger using hot water entering at 97 °C and leaving at 65 °C. Specific heat of juice and water are 3.8 kJ.kg$^{-1}$.K$^{-1}$ and 4.2 kJ.kg$^{-1}$.K$^{-1}$, respectively. Flow rate of juice is 0.3 kg.s$^{-1}$ and that of water is 0.4 kg.s$^{-1}$. Considering an overall heat transfer coefficient of 1 kW.m$^{-2}$.K$^{-1}$, the area of heat exchanger required, in m$^2$, is _________. (Rounded off to 3 decimal places)
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App