This solution determines the Number of Transfer Units (NTU) for a counter-current double pipe heat exchanger (DPHE) using the provided effectiveness and heat capacity ratio.
The essential parameters given are:
For counter-current flow where the heat capacity ratio $C_r$ equals 1, the effectiveness ($\epsilon$) is related to the Number of Transfer Units (NTU) by the following equation:
$ \epsilon = \frac{NTU}{NTU + 1} $The calculated NTU value of approximately 1.857 falls within the specified range.
The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________