In a counter-current flow double pipe heat exchanger (DPHE), temperature difference between the hot and cold liquids at all positions is held constant at C. If the effectiveness of the heat exchanger is 0.65 and heat capacity ratio of hot and cold liquids is 1, the number of transfer units (NTU) is ________.

Heat Exchanger NTU Calculation

This solution determines the Number of Transfer Units (NTU) for a counter-current double pipe heat exchanger (DPHE) using the provided effectiveness and heat capacity ratio.

Problem Analysis

The essential parameters given are:

  • Heat Exchanger Type: Counter-current DPHE
  • Effectiveness ($\epsilon$): 0.65
  • Heat Capacity Ratio ($C_r = C_h / C_c$): 1
  • Condition: Constant temperature difference ($C$) between hot and cold fluids throughout. This condition simplifies to the standard effectiveness formula for $C_r = 1$ in counter-current flow.

Effectiveness-NTU Relation

For counter-current flow where the heat capacity ratio $C_r$ equals 1, the effectiveness ($\epsilon$) is related to the Number of Transfer Units (NTU) by the following equation:

$ \epsilon = \frac{NTU}{NTU + 1} $

Calculation Steps

  1. Input Effectiveness: Substitute the given effectiveness value ($\epsilon = 0.65$) into the formula. $ 0.65 = \frac{NTU}{NTU + 1} $
  2. Algebraic Rearrangement: Solve the equation for NTU. Multiply both sides by $(NTU + 1)$: $ 0.65 \times (NTU + 1) = NTU $ Distribute 0.65: $ 0.65 \times NTU + 0.65 = NTU $ Group NTU terms: $ 0.65 = NTU - 0.65 \times NTU $ Factor out NTU: $ 0.65 = NTU \times (1 - 0.65) $ $ 0.65 = NTU \times 0.35 $
  3. Compute NTU: Divide to find the final value. $ NTU = \frac{0.65}{0.35} $ Simplify the fraction: $ NTU = \frac{65}{35} = \frac{13}{7} $ $ NTU \approx 1.857 $

The calculated NTU value of approximately 1.857 falls within the specified range.

Was this answer helpful?

Important Questions from Heat Exchangers

  1. Milk enters into the heating section of a high temperature short time (HTST) pasteurization plant at a temperature of $45^\circ C$ and leaves at $72^\circ C$. Hot water at temperature of $95 \text{ }^\circ C$ enters counter- currently into the heat exchanger and leaves at $77^\circ C$. The effectiveness of the heat exchanger is
  2. The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________

  3. Hot refined oil at $120 \text{ °C}$ enters a concentric tube-in-tube heat exchanger (HE) at the rate of $20 \text{ kg min}^{-1}$. The oil is cooled by water entering at a temperature of $30 \text{ °C}$ from the other end of the HE at the rate of $50 \text{ kg min}^{-1}$. Specific heat capacities of oil and water are $1.9$ and $4.2 \text{ kJ kg}^{-1} \text{ °C}^{-1}$, respectively. The effectiveness of the HE may be taken as $0.7$. Assuming no heat loss to the surrounding under steady-state condition, the exit temperature of water from the HE in $ \text{°C}$ is
  4. Fruit juice entering at 30 °C is being pasteurized in a double pipe counter flow heat exchanger using hot water entering at 97 °C and leaving at 65 °C. Specific heat of juice and water are 3.8 kJ.kg$^{-1}$.K$^{-1}$ and 4.2 kJ.kg$^{-1}$.K$^{-1}$, respectively. Flow rate of juice is 0.3 kg.s$^{-1}$ and that of water is 0.4 kg.s$^{-1}$. Considering an overall heat transfer coefficient of 1 kW.m$^{-2}$.K$^{-1}$, the area of heat exchanger required, in m$^2$, is _________. (Rounded off to 3 decimal places)
  5. The log mean temperature difference (LMTD) correction factor is not required during heat transfer rate calculation in
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App