Heat Exchanger Effectiveness Analysis
This solution calculates the exit temperature of water in a concentric tube heat exchanger using the given effectiveness.
Given Data
- Hot Fluid (Oil): Inlet Temperature ($T_{h,in}$) = $120 \text{ °C}$
- Hot Fluid (Oil): Mass Flow Rate ($\dot{m}_h$) = $20 \text{ kg min}^{-1}$
- Hot Fluid (Oil): Specific Heat ($C_{p,h}$) = $1.9 \text{ kJ kg}^{-1} \text{ °C}^{-1}$
- Cold Fluid (Water): Inlet Temperature ($T_{c,in}$) = $30 \text{ °C}$
- Cold Fluid (Water): Mass Flow Rate ($\dot{m}_c$) = $50 \text{ kg min}^{-1}$
- Cold Fluid (Water): Specific Heat ($C_{p,c}$) = $4.2 \text{ kJ kg}^{-1} \text{ °C}^{-1}$
- Heat Exchanger Effectiveness ($\epsilon$) = $0.7$
- Assumptions: Steady-state, no heat loss.
Calculations
Step 1: Calculate Heat Capacity Rates
The heat capacity rate ($C$) is the product of mass flow rate ($\dot{m}$) and specific heat capacity ($C_p$).
- For oil ($C_h$):
$C_h = \dot{m}_h \times C_{p,h} = (20 \text{ kg min}^{-1}) \times (1.9 \text{ kJ kg}^{-1} \text{ °C}^{-1}) = 38 \text{ kJ min}^{-1} \text{ °C}^{-1}$
- For water ($C_c$):
$C_c = \dot{m}_c \times C_{p,c} = (50 \text{ kg min}^{-1}) \times (4.2 \text{ kJ kg}^{-1} \text{ °C}^{-1}) = 210 \text{ kJ min}^{-1} \text{ °C}^{-1}$
Step 2: Identify Minimum Heat Capacity Rate ($C_{min}$)
The minimum heat capacity rate determines the maximum possible heat transfer.
- Comparing $C_h$ and $C_c$: $C_{min} = \min(38, 210) = 38 \text{ kJ min}^{-1} \text{ °C}^{-1}$.
- The hot fluid (oil) has the minimum heat capacity rate ($C_h = C_{min}$).
Step 3: Calculate Maximum Possible Heat Transfer ($Q_{max}$)
Maximum heat transfer occurs when the fluid with $C_{min}$ undergoes the maximum possible temperature change (from hot inlet to cold inlet temperature).
- $Q_{max} = C_{min} \times (T_{h,in} - T_{c,in})$
$Q_{max} = (38 \text{ kJ min}^{-1} \text{ °C}^{-1}) \times (120 \text{ °C} - 30 \text{ °C})$
$Q_{max} = 38 \times 90 \text{ kJ min}^{-1} = 3420 \text{ kJ min}^{-1}$
Step 4: Calculate Actual Heat Transfer Rate ($Q$)
The actual heat transfer is related to the maximum possible heat transfer by the effectiveness ($\epsilon$).
- $\epsilon = \frac{Q}{Q_{max}}$
- $Q = \epsilon \times Q_{max} = 0.7 \times 3420 \text{ kJ min}^{-1} = 2394 \text{ kJ min}^{-1}$
Step 5: Calculate Water Exit Temperature ($T_{c,out}$)
The actual heat gained by the cold fluid (water) equals the actual heat transfer rate ($Q$).
- $Q = \dot{m}_c \times C_{p,c} \times (T_{c,out} - T_{c,in})$
$2394 \text{ kJ min}^{-1} = (210 \text{ kJ min}^{-1} \text{ °C}^{-1}) \times (T_{c,out} - 30 \text{ °C})$
- Solve for $T_{c,out}$:
$T_{c,out} - 30 \text{ °C} = \frac{2394 \text{ kJ min}^{-1}}{210 \text{ kJ min}^{-1} \text{ °C}^{-1}}$
$T_{c,out} - 30 \text{ °C} = 11.4 \text{ °C}$
$T_{c,out} = 11.4 \text{ °C} + 30 \text{ °C} = 41.4 \text{ °C}$
Conclusion
The exit temperature of the water from the heat exchanger is $41.4 \text{ °C}$.