Question

The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________

Calculate Heat Exchanger Fouling Coefficient

Fouling in a heat exchanger adds thermal resistance, which reduces the overall heat transfer coefficient ($U$). The decrease in $U$ is directly related to the fouling resistance.

Identify Given Values

  • Initial overall heat transfer coefficient (clean), $U_1 = 1000 \text{ W m}^{-2} \text{ K}^{-1}$
  • Final overall heat transfer coefficient (fouled), $U_2 = 800 \text{ W m}^{-2} \text{ K}^{-1}$

Calculate Fouling Resistance

The thermal resistance is the reciprocal of the heat transfer coefficient. Fouling increases the total resistance.

The increase in resistance due to fouling ($R_f$) is calculated as:

$ R_f = R_{fouled} - R_{clean} = \frac{1}{U_2} - \frac{1}{U_1} $

Substitute the given values:

$ R_f = \frac{1}{800 \text{ W m}^{-2} \text{ K}^{-1}} - \frac{1}{1000 \text{ W m}^{-2} \text{ K}^{-1}} $

To subtract the fractions, find a common denominator:

$ R_f = \frac{1000 - 800}{(800)(1000)} \text{ m}^2 \text{ K W}^{-1} $

$ R_f = \frac{200}{800000} \text{ m}^2 \text{ K W}^{-1} $

$ R_f = \frac{1}{4000} \text{ m}^2 \text{ K W}^{-1} $

Determine Fouling Film Coefficient

The fouling film coefficient ($h_f$) is related to the fouling resistance ($R_f$) by the equation:

$ R_f = \frac{1}{h_f} $

Therefore, the fouling film coefficient is:

$ h_f = \frac{1}{R_f} $

$ h_f = \frac{1}{\frac{1}{4000} \text{ m}^2 \text{ K W}^{-1}} $

$ h_f = 4000 \text{ W m}^{-2} \text{ K}^{-1} $

Final Answer

The fouling film coefficient for the heat exchanger is $4000 \text{ W m}^{-2} \text{ K}^{-1}$.

Was this answer helpful?

Important Questions from Heat Exchangers

  1. In a counter-current flow double pipe heat exchanger (DPHE), temperature difference between the hot and cold liquids at all positions is held constant at C. If the effectiveness of the heat exchanger is 0.65 and heat capacity ratio of hot and cold liquids is 1, the number of transfer units (NTU) is ________.
  2. Milk enters into the heating section of a high temperature short time (HTST) pasteurization plant at a temperature of $45^\circ C$ and leaves at $72^\circ C$. Hot water at temperature of $95 \text{ }^\circ C$ enters counter- currently into the heat exchanger and leaves at $77^\circ C$. The effectiveness of the heat exchanger is
  3. Hot refined oil at $120 \text{ °C}$ enters a concentric tube-in-tube heat exchanger (HE) at the rate of $20 \text{ kg min}^{-1}$. The oil is cooled by water entering at a temperature of $30 \text{ °C}$ from the other end of the HE at the rate of $50 \text{ kg min}^{-1}$. Specific heat capacities of oil and water are $1.9$ and $4.2 \text{ kJ kg}^{-1} \text{ °C}^{-1}$, respectively. The effectiveness of the HE may be taken as $0.7$. Assuming no heat loss to the surrounding under steady-state condition, the exit temperature of water from the HE in $ \text{°C}$ is
  4. Fruit juice entering at 30 °C is being pasteurized in a double pipe counter flow heat exchanger using hot water entering at 97 °C and leaving at 65 °C. Specific heat of juice and water are 3.8 kJ.kg$^{-1}$.K$^{-1}$ and 4.2 kJ.kg$^{-1}$.K$^{-1}$, respectively. Flow rate of juice is 0.3 kg.s$^{-1}$ and that of water is 0.4 kg.s$^{-1}$. Considering an overall heat transfer coefficient of 1 kW.m$^{-2}$.K$^{-1}$, the area of heat exchanger required, in m$^2$, is _________. (Rounded off to 3 decimal places)
  5. The log mean temperature difference (LMTD) correction factor is not required during heat transfer rate calculation in
Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App