This solution calculates the log-mean temperature correction factor ($F$) for the given plate heat exchanger scenario.
First, calculate the heat absorbed by the fruit juice using its mass flow rate ($\dot{m}_j$), specific heat capacity ($c_{p,j}$), and temperature change ($\Delta T_j$).
Given:
Calculation:
$ Q = \dot{m}_j c_{p,j} (T_{j,out} - T_{j,in}) $
$ Q = (2 \text{ kg s}^{-1}) \times (3.7 \text{ kJ kg}^{-1} \text{ K}^{-1}) \times (75^{\circ}C - 45^{\circ}C) $
$ Q = 2 \times 3.7 \times 30 = 222 \text{ kJ s}^{-1} = 222000 \text{ W} $
Determine the temperature differences at the two ends of the heat exchanger.
Given:
End 1 temperature difference ($\Delta T_1$):
$ \Delta T_1 = T_{w,in} - T_{j,out} = 95^{\circ}C - 75^{\circ}C = 20^{\circ}C $
End 2 temperature difference ($\Delta T_2$):
$ \Delta T_2 = T_{w,out} - T_{j,in} = 70^{\circ}C - 45^{\circ}C = 25^{\circ}C $
Use the calculated temperature differences to find the LMTD ($\Delta T_{lm}$).
$ \Delta T_{lm} = \frac{\Delta T_1 - \Delta T_2}{\ln(\Delta T_1 / \Delta T_2)} $
$ \Delta T_{lm} = \frac{20^{\circ}C - 25^{\circ}C}{\ln(20^{\circ}C / 25^{\circ}C)} = \frac{-5^{\circ}C}{\ln(0.8)} $
$ \Delta T_{lm} \approx \frac{-5}{-0.22314} \approx 22.41^{\circ}C $
Use the overall heat transfer equation $Q = U A F \Delta T_{lm}$ to solve for the correction factor ($F$).
Given:
Rearranging the formula for $F$:
$ F = \frac{Q}{U A \Delta T_{lm}} $
$ F = \frac{222000 \text{ W}}{(1122 \text{ W m}^{-2} \text{ K}^{-1}) \times (12.75 \text{ m}^2) \times (22.41 \text{ K})} $
$ F \approx \frac{222000}{321757.575} \approx 0.690 $
The calculated correction factor ($F \approx 0.690$) falls within the expected range.
The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________