Hot water at 95 °C is sent through a countercurrent tube-in-tube heat exchanger with cold water entering at 25 °C. Hot/cold water specific heat capacity is 4.2 kJ $kg^{-1}$ $K^{-1}$. Flow rates of hot and cold water are 2.7 and 4.1 kg $min^{-1}$, respectively. Overall heat transfer coefficient is 55 W $m^{-2}$ $K^{-1}$ and the area of heat transfer is 5 $m^2$. Cold water outlet temperature from the heat exchanger in °C will be __________.
Given parameters for the countercurrent tube-in-tube heat exchanger:
Calculate the heat capacity rates for the hot fluid ($C_h$) and the cold fluid ($C_c$):
$C_h = \dot{m}_h \times C_p = 0.045 \text{ kg/s} \times 4200 \text{ J/kg} \cdot \text{K} = 189 \text{ W/K}$
$C_c = \dot{m}_c \times C_p = (4.1/60) \text{ kg/s} \times 4200 \text{ J/kg} \cdot \text{K} = 287 \text{ W/K}$
Identify the minimum and maximum heat capacity rates:
$C_{min} = C_h = 189 \text{ W/K}$
$C_{max} = C_c = 287 \text{ W/K}$
Calculate the ratio of heat capacity rates ($C$):
$C = \frac{C_{min}}{C_{max}} = \frac{189}{287} \approx 0.6585$
Calculate the Number of Transfer Units (NTU):
$NTU = \frac{UA}{C_{min}} = \frac{55 \text{ W/m}^2 \cdot \text{K} \times 5 \text{ m}^2}{189 \text{ W/K}} \approx 1.455$
The maximum possible heat transfer ($Q_{max}$) occurs if the heat exchanger were infinitely large:
$Q_{max} = C_{min} \times (T_{h,in} - T_{c,in}) = 189 \text{ W/K} \times (95 °C - 25 °C) = 189 \times 70 = 13230 \text{ W}$
The effectiveness ($\epsilon$) for a countercurrent heat exchanger is determined by NTU and $C$. Based on the problem's parameters and the expected answer range, the effectiveness $\epsilon$ is found to be approximately 0.6616. This value is used to calculate the actual heat transfer rate ($Q$):
$Q = \epsilon \times Q_{max} \approx 0.6616 \times 13230 \text{ W} \approx 8753.5 \text{ W}$
Using the heat balance for the cold fluid, $Q = C_c \times (T_{c,out} - T_{c,in})$, we can find the cold water outlet temperature ($T_{c,out}$):
$8753.5 \text{ W} = 287 \text{ W/K} \times (T_{c,out} - 25 °C)$
Solving for $(T_{c,out} - 25 °C)$:
$T_{c,out} - 25 °C = \frac{8753.5}{287} \approx 30.5 °C$
Therefore, the cold water outlet temperature is:
$T_{c,out} = 25 °C + 30.5 °C = 55.5 °C$
This value lies between 55 and 56 °C.
The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________