This solution determines the Log-Mean Temperature Difference (LMTD) and compares it with the Arithmetic Mean Temperature Difference (AMTD) for a counter-flow heat exchanger, using the provided parameters for heating oil with hot water.
The operating conditions for the heat exchanger are:
Calculate the temperature differences at the inlet and outlet sides:
The Arithmetic Mean Temperature Difference (AMTD) is the average of the two end differences:
$ \text{AMTD} = \frac{\Delta T_1 + \Delta T_2}{2} $
$ \text{AMTD} = \frac{23 \text{ }^\circ\text{C} + 35 \text{ }^\circ\text{C}}{2} = \frac{58 \text{ }^\circ\text{C}}{2} = 29 \text{ }^\circ\text{C} $
The Log-Mean Temperature Difference (LMTD) is calculated using the formula:
$ \text{LMTD} = \frac{\Delta T_1 - \Delta T_2}{\ln\left(\frac{\Delta T_1}{\Delta T_2}\right)} $
$ \text{LMTD} = \frac{23 \text{ }^\circ\text{C} - 35 \text{ }^\circ\text{C}}{\ln\left(\frac{23}{35}\right)} = \frac{-12 \text{ }^\circ\text{C}}{\ln(0.65714)} \approx \frac{-12 \text{ }^\circ\text{C}}{-0.4203} \approx 28.55 \text{ }^\circ\text{C} $
The calculated values are:
The LMTD ($28.55 \text{ }^\circ\text{C}$) is slightly smaller than the AMTD ($29 \text{ }^\circ\text{C}$). The difference ($0.45 \text{ }^\circ\text{C}$) is small relative to the values themselves.
This closeness occurs because the temperature differences at the ends ($23 \text{ }^\circ\text{C}$ and $35 \text{ }^\circ\text{C}$) are not vastly different. In a counter-flow heat exchanger, LMTD equals AMTD only if $\Delta T_1 = \Delta T_2$. As the ratio $\frac{\Delta T_1}{\Delta T_2}$ approaches 1, LMTD approaches AMTD. Therefore, the LMTD is very nearly equal to the AMTD.
| Parameter | Symbol | Value |
|---|---|---|
| Hot Fluid Inlet Temp. | $T_{h,in}$ | $100 \text{ }^\circ\text{C}$ |
| Hot Fluid Outlet Temp. | $T_{h,out}$ | $70 \text{ }^\circ\text{C}$ |
| Cold Fluid Inlet Temp. | $T_{c,in}$ | $35 \text{ }^\circ\text{C}$ |
| Cold Fluid Outlet Temp. | $T_{c,out}$ | $77 \text{ }^\circ\text{C}$ |
| Temp. Diff. End 1 ($\Delta T_1$) | $23 \text{ }^\circ\text{C}$ | |
| Temp. Diff. End 2 ($\Delta T_2$) | $35 \text{ }^\circ\text{C}$ | |
| AMTD | $29 \text{ }^\circ\text{C}$ | |
| LMTD | $\approx 28.55 \text{ }^\circ\text{C}$ |
The overall heat transfer coefficient based on the outside surface area of a tubular heat exchanger decreased due to fouling during operation from $1000 \text{ W m}^{-2} \text{ K}^{-1}$ to $800 \text{ W m}^{-2} \text{ K}^{-1}$. The fouling film coefficient of the heat exchanger in $\text{W m}^{-2} \text{ K}^{-1}$ is________