Which of the following heat exchangers gives parallel and linear temperature profile for both cold and hot fluid?
Counter flow with equal heat capacities
Understanding the temperature profiles of fluids within a heat exchanger is crucial for analyzing its performance and efficiency. A "parallel and linear temperature profile" for both hot and cold fluids implies that the temperature difference between the two fluids remains constant throughout the length of the heat exchanger, and the temperature of each fluid changes uniformly along its path.
For temperature profiles to be both parallel and linear in a heat exchanger, two primary conditions must be met:
The heat transfer rate \( (dQ) \) over a differential area \( (dA) \) is given by:
\[ dQ = U dA (T_h - T_c) \]
Where \( U \) is the overall heat transfer coefficient.
From the energy balance for each fluid, the heat transferred also relates to the change in temperature:
\[ dQ = -\dot{m}_h C_{p,h} dT_h \]
\[ dQ = \dot{m}_c C_{p,c} dT_c \]
Here, \( \dot{m} \) is the mass flow rate and \( C_p \) is the specific heat capacity. The product \( \dot{m}C_p \) is known as the heat capacity rate, often denoted as \( C \). So, \( C_h = \dot{m}_h C_{p,h} \) and \( C_c = \dot{m}_c C_{p,c} \).
In a parallel flow heat exchanger, both fluids enter from the same end and flow in the same direction. When the heat capacity rates \( (C_h \neq C_c) \) are unequal, the temperatures of the hot and cold fluids approach each other. The temperature difference \( (\Delta T) \) continuously decreases along the length of the heat exchanger. The temperature profiles in this case are curved and therefore not parallel or linear.
Even with equal heat capacity rates \( (C_h = C_c) \) in a parallel flow configuration, the temperature difference still continuously decreases as the fluids exchange heat. They would approach a common equilibrium temperature. The temperature profiles would still be curved and not parallel or linear.
Crossed flow heat exchangers involve fluids flowing perpendicular to each other. Their temperature profiles are generally complex and not linear or parallel, especially with unequal heat capacities, due to the varying local temperature differences across the heat transfer area.
This is the specific case where the temperature profiles are parallel and linear. In a counter flow heat exchanger, the hot and cold fluids flow in opposite directions.
If the heat capacity rates of both fluids are equal \( (C_h = C_c) \), then the temperature difference \( (\Delta T = T_h - T_c) \) between the hot and cold fluids remains constant along the entire length of the heat exchanger.
Consider the change in temperature for each fluid over a differential heat transfer \( dQ \):
\[ dT_h = -\frac{dQ}{C_h} \]
\[ dT_c = \frac{dQ}{C_c} \]
If \( C_h = C_c \), then \( |dT_h| = |dT_c| \) for the same amount of heat transfer \( dQ \). This means that for every unit of heat transferred, the temperature of the hot fluid drops by the same amount that the cold fluid's temperature rises. Since they flow in opposite directions, this results in the temperature difference \( (T_h - T_c) \) staying constant.
Because the temperature difference is constant \( (\Delta T = \text{constant}) \), the temperature profiles are parallel. And since the heat capacity rates are constant and the heat transfer coefficient is assumed uniform, the rate of temperature change for each fluid is also constant, leading to linear temperature profiles.
Based on the analysis, only a counter flow heat exchanger where the heat capacity rates of both the hot and cold fluids are equal \( (\dot{m}_h C_{p,h} = \dot{m}_c C_{p,c}) \) will exhibit parallel and linear temperature profiles. This unique condition ensures that the temperature difference remains constant throughout the exchanger, leading to the characteristic linear and parallel temperature lines.
For a double pipe counter flow heat exchanger with \(\rm \frac{C_{Min}}{C_{Max}}=1\) , the effective of heat exchanger is
A fan is provided in the water cooling system to
Heat exchangers are used in
A. Condensers and boilers in steam plants
B. Radiators
C. Intercoolers and preheaters
D. Condensers and evaporators in refrigerators and air conditioners
In gas turbine, hot exhaust gases are used to heat the compresses air in a compact heat exchanger with effectiveness 0.8. What is the value of NTU?
Effectiveness of heat exchanger is function of: