For a balanced counter flow heat exchanger where ṁ h Cp h = ṁ c Cp c , the logarithmic mean temperature difference (LMTD) and temperature profile is:
A heat exchanger facilitates the transfer of thermal energy between two fluids at different temperatures. A counter-flow heat exchanger is a type where the two fluids flow in opposite directions. A 'balanced' counter-flow heat exchanger is specifically characterized by the condition where the heat capacity rate of the hot fluid ($\dot{m}_h C_{p_h}$) is equal to the heat capacity rate of the cold fluid ($\dot{m}_c C_{p_c}$). This condition has significant implications for the temperature profile and the logarithmic mean temperature difference (LMTD).
The given condition is:
$\dot{m}_h C_{p_h} = \dot{m}_c C_{p_c}$
This is equivalent to stating that the heat capacity rate of the hot fluid ($C_h$) is equal to the heat capacity rate of the cold fluid ($C_c$), i.e., $C_h = C_c = C$.
Consider a differential section $dA$ of the heat exchanger. The heat transferred in this section is $dQ$. According to the energy balance for each fluid:
Since $C_h = C_c = C$, we have $-C dT_h = C dT_c$, which simplifies to $dT_h = -dT_c$.
Integrating this relationship over the length of the heat exchanger, considering the total temperature change for each fluid:
$\int_{T_{h,out}}^{T_{h,in}} dT_h = -\int_{T_{c,in}}^{T_{c,out}} dT_c$
$T_{h,in} - T_{h,out} = -(T_{c,out} - T_{c,in})$
$T_{h,in} - T_{h,out} = T_{c,in} - T_{c,out}$
Rearranging this gives:
$T_{h,in} + T_{c,out} = T_{h,out} + T_{c,in}$
Now, let's consider the temperature difference ($\Delta T$) at the two ends of the counter-flow heat exchanger. Let end 1 be where the hot fluid enters and the cold fluid exits, and end 2 be where the hot fluid exits and the cold fluid enters.
From the energy balance $T_{h,in} + T_{c,out} = T_{h,out} + T_{c,in}$, we can rearrange it to show that $\Delta T_1 = \Delta T_2$:
$T_{h,in} - T_{c,out} = T_{h,out} - T_{c,in}$
Thus, the temperature difference between the hot and cold fluids is the same at both ends of a balanced counter-flow heat exchanger. Let this constant difference be $\Delta T_{const}$.
If the temperature difference at the two ends of a counter-flow exchanger is equal, and the temperature change of each fluid per unit heat transfer is constant (as $C_h$ and $C_c$ are constant), it implies that the temperature difference between the hot and cold fluids remains constant along the entire length of the heat exchanger. That is, $\Delta T(x) = T_h(x) - T_c(x) = \Delta T_{const}$ for all $x$ along the flow path.
The rate of heat transfer through a differential area $dA$ is given by $dQ = U dA \Delta T$, where $U$ is the overall heat transfer coefficient. If we assume $U$ is constant and we have shown that $\Delta T$ is constant along the length, then $dQ/dA = U \Delta T_{const}$ is constant. Since $dQ = -C_h dT_h = C_c dT_c$, and $C_h=C_c=C$ are constant, we have $dT_h = -dQ/C$ and $dT_c = dQ/C$. If $dQ/dA$ is constant, and assuming area $A$ varies linearly with length $x$ (i.e., $dA = P dx$ where $P$ is the perimeter), then $dQ/dx$ is also constant. This implies that $dT_h/dx$ and $dT_c/dx$ are constant. A constant derivative means that $T_h$ and $T_c$ vary linearly with the length along the heat exchanger.
Since $T_h(x)$ and $T_c(x)$ are linear functions of $x$, their graphs are straight lines. As the difference between these two functions, $\Delta T(x) = T_h(x) - T_c(x)$, is constant along the length, the two straight lines representing the temperature profiles of the hot and cold fluids on a temperature vs. length graph will be parallel to each other.
The LMTD is defined as:
$\text{LMTD} = \frac{\Delta T_1 - \Delta T_2}{\ln(\Delta T_1 / \Delta T_2)}$
When $\Delta T_1 = \Delta T_2 = \Delta T_{const}$, this formula becomes indeterminate ($0/0$). Using L'Hopital's rule or taking the limit as $\Delta T_1 \to \Delta T_2$, it can be shown that the LMTD is equal to the constant temperature difference:
$\text{LMTD} = \Delta T_{const}$
Based on this analysis, the characteristics of a balanced counter flow heat exchanger are: $\Delta T$ at any section is Constant, the temperature profiles are Parallel, and they are Linear.
Comparing this with the given options:
Therefore, the correct description is that the temperature difference at any section is constant, and the temperature profile lines are parallel and linear.
Heat exchangers are used in
A. Condensers and boilers in steam plants
B. Radiators
C. Intercoolers and preheaters
D. Condensers and evaporators in refrigerators and air conditioners
For a specified inlet and outlet temperatures, for which kind of heat exchange will the log mean temperature difference, ΔTlm will be highest?
The fouling factor in case of heat exchangers is given by ________
In heat transfe,r NTU is given by ________.
(Where U = heat transfer co-efficient, A = surface area, C = Heat capacitance, min = Minimum, max = Maximum
Which of the following heat exchangers gives parallel and linear temperature profile for both cold and hot fluid?