For a specified inlet and outlet temperatures, for which kind of heat exchange will the log mean temperature difference, ΔTlm will be highest?
Double pipe counter flow heat exchanger
The Log Mean Temperature Difference (LMTD) is a crucial parameter in heat exchanger calculations. It represents the average temperature difference between the hot and cold fluids across the heat exchanger, driving the heat transfer process. A higher LMTD indicates a more effective heat exchange for given flow rates and fluid properties.
The LMTD is calculated using the formula:
$$ LMTD = \frac{\Delta T_1 - \Delta T_2}{\ln(\Delta T_1 / \Delta T_2)} $$
Where $\Delta T_1$ and $\Delta T_2$ are the temperature differences between the hot and cold streams at the two respective ends of the heat exchanger.
The way fluids flow relative to each other significantly impacts the LMTD. The primary arrangements considered are:
For a given set of inlet and outlet temperatures for both the hot fluid ($T_{h,in}$, $T_{h,out}$) and the cold fluid ($T_{c,in}$, $T_{c,out}$), the counter-flow arrangement generally yields the highest LMTD.
Let's compare the terminal temperature differences:
Consider an example:
| Parameter | Value |
|---|---|
| Hot Inlet ($T_{h,in}$) | 100 $^\circ$C |
| Hot Outlet ($T_{h,out}$) | 60 $^\circ$C |
| Cold Inlet ($T_{c,in}$) | 20 $^\circ$C |
| Cold Outlet ($T_{c,out}$) | 50 $^\circ$C |
For this example:
As seen, $LMTD_{counter} > LMTD_{parallel}$. The counter-flow arrangement maintains a higher average temperature difference.
Crossflow and multi-pass heat exchangers typically have an LMTD that falls between the parallel and counter-flow values. Their performance is often evaluated using a correction factor, '$F$', applied to the pure counter-flow LMTD: $LMTD_{corrected} = F \times LMTD_{counterflow}$. Since '$F$' is usually less than 1 for these configurations, their effective LMTD is lower than that of a pure counter-flow system with the same terminal temperatures.
Therefore, for specified inlet and outlet temperatures, the double pipe counter flow heat exchanger provides the highest Log Mean Temperature Difference (LMTD), leading to potentially higher thermal efficiency or a more compact design compared to other arrangements.
For a double pipe counter flow heat exchanger with \(\rm \frac{C_{Min}}{C_{Max}}=1\) , the effective of heat exchanger is
A fan is provided in the water cooling system to
Heat exchangers are used in
A. Condensers and boilers in steam plants
B. Radiators
C. Intercoolers and preheaters
D. Condensers and evaporators in refrigerators and air conditioners
In gas turbine, hot exhaust gases are used to heat the compresses air in a compact heat exchanger with effectiveness 0.8. What is the value of NTU?
Effectiveness of heat exchanger is function of: