For a specified inlet and outlet temperatures, for which kind of heat exchange will the log mean temperature difference, ΔTlm will be highest?

The correct answer is

Double pipe counter flow heat exchanger

Understanding Log Mean Temperature Difference (LMTD)

The Log Mean Temperature Difference (LMTD) is a crucial parameter in heat exchanger calculations. It represents the average temperature difference between the hot and cold fluids across the heat exchanger, driving the heat transfer process. A higher LMTD indicates a more effective heat exchange for given flow rates and fluid properties.

The LMTD is calculated using the formula:

$$ LMTD = \frac{\Delta T_1 - \Delta T_2}{\ln(\Delta T_1 / \Delta T_2)} $$

Where $\Delta T_1$ and $\Delta T_2$ are the temperature differences between the hot and cold streams at the two respective ends of the heat exchanger.

Comparing Heat Exchanger Flow Arrangements

The way fluids flow relative to each other significantly impacts the LMTD. The primary arrangements considered are:

  • Parallel Flow: In this setup, both the hot and cold fluids flow in the same direction through the heat exchanger. The temperature difference is largest at the inlet and decreases along the length, becoming smallest at the outlet.
  • Counter Flow: Here, the hot and cold fluids flow in opposite directions. This arrangement allows for a more sustained temperature difference between the fluids along the entire length of the exchanger. Ideally, the cold fluid exits hotter than the hot fluid exits, although this requires specific conditions.
  • Crossflow: Fluids flow roughly perpendicular to each other. This is common in applications like car radiators.
  • Multi-pass: This involves routing the fluids through the exchanger multiple times, often to enhance heat transfer or compactness.

LMTD Maximization with Counter Flow

For a given set of inlet and outlet temperatures for both the hot fluid ($T_{h,in}$, $T_{h,out}$) and the cold fluid ($T_{c,in}$, $T_{c,out}$), the counter-flow arrangement generally yields the highest LMTD.

Let's compare the terminal temperature differences:

  • Parallel Flow: The temperature differences at the ends are $\Delta T_1 = T_{h,in} - T_{c,in}$ and $\Delta T_2 = T_{h,out} - T_{c,out}$.
  • Counter Flow: The temperature differences at the ends are $\Delta T_1 = T_{h,in} - T_{c,out}$ and $\Delta T_2 = T_{h,out} - T_{c,in}$.

Consider an example:

Example Temperatures
Parameter Value
Hot Inlet ($T_{h,in}$) 100 $^\circ$C
Hot Outlet ($T_{h,out}$) 60 $^\circ$C
Cold Inlet ($T_{c,in}$) 20 $^\circ$C
Cold Outlet ($T_{c,out}$) 50 $^\circ$C

For this example:

  • Parallel Flow: $\Delta T_1 = 100 - 20 = 80^\circ$C, $\Delta T_2 = 60 - 50 = 10^\circ$C. $LMTD_{parallel} = \frac{80 - 10}{\ln(80/10)} \approx 33.67^\circ$C.
  • Counter Flow: $\Delta T_1 = 100 - 50 = 50^\circ$C, $\Delta T_2 = 60 - 20 = 40^\circ$C. $LMTD_{counter} = \frac{50 - 40}{\ln(50/40)} \approx 44.84^\circ$C.

As seen, $LMTD_{counter} > LMTD_{parallel}$. The counter-flow arrangement maintains a higher average temperature difference.

Performance of Other Flow Arrangements

Crossflow and multi-pass heat exchangers typically have an LMTD that falls between the parallel and counter-flow values. Their performance is often evaluated using a correction factor, '$F$', applied to the pure counter-flow LMTD: $LMTD_{corrected} = F \times LMTD_{counterflow}$. Since '$F$' is usually less than 1 for these configurations, their effective LMTD is lower than that of a pure counter-flow system with the same terminal temperatures.

Conclusion

Therefore, for specified inlet and outlet temperatures, the double pipe counter flow heat exchanger provides the highest Log Mean Temperature Difference (LMTD), leading to potentially higher thermal efficiency or a more compact design compared to other arrangements.

Was this answer helpful?

Important Questions from Heat Exchanger

  1. For a double pipe counter flow heat exchanger with \(\rm \frac{C_{Min}}{C_{Max}}=1\) , the effective of heat exchanger is

  2. A fan is provided in the water cooling system to

  3. Heat exchangers are used in

    A. Condensers and boilers in steam plants

    B. Radiators

    C. Intercoolers and preheaters

    D. Condensers and evaporators in refrigerators and air conditioners

  4. In gas turbine, hot exhaust gases are used to heat the compresses air in a compact heat exchanger with effectiveness 0.8. What is the value of NTU?

  5. Effectiveness of heat exchanger is function of:

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App