Question

What is the percentage saving in feeder copper if the line voltage in a 2-wire DC systems is raised from 100 V to 200 V for the same power transmitted over the same power distance and having the same power loss?

The correct answer is

75%

Percentage Saving in Feeder Copper Calculation

To determine the percentage saving in feeder copper when the line voltage is increased, we need to analyze the relationships between power transmitted, current, power loss, resistance, and the physical dimensions (cross-sectional area) of the copper conductors, assuming the transmission distance and power loss remain constant.

Let the initial voltage be \(V_1 = 100\) V and the increased voltage be \(V_2 = 200\) V. Let \(P\) be the constant power transmitted and \(P_{loss}\) be the constant power loss in the feeder. Let \(I_1\) and \(I_2\) be the currents at voltages \(V_1\) and \(V_2\), respectively. Let \(R_1\) and \(R_2\) be the total resistances of the 2-wire feeder at voltages \(V_1\) and \(V_2\), respectively.

Relationship between Power, Voltage, and Current

The power transmitted \(P\) in a DC system is given by: \[P = V \times I\] Since \(P\) is constant: \[P = V_1 I_1 = V_2 I_2\] \[\frac{I_2}{I_1} = \frac{V_1}{V_2}\] Given \(V_1 = 100\) V and \(V_2 = 200\) V: \[\frac{I_2}{I_1} = \frac{100}{200} = \frac{1}{2}\] So, the new current \(I_2\) is half of the original current \(I_1\): \(I_2 = \frac{I_1}{2}\).

Relationship between Power Loss, Current, and Resistance

The power loss \(P_{loss}\) in the feeder resistance is given by: \[P_{loss} = I^2 R\] Since the power loss \(P_{loss}\) is constant: \[P_{loss} = I_1^2 R_1 = I_2^2 R_2\] Substitute \(I_2 = \frac{I_1}{2}\): \[I_1^2 R_1 = \left(\frac{I_1}{2}\right)^2 R_2\] \[I_1^2 R_1 = \frac{I_1^2}{4} R_2\] Assuming \(I_1 \neq 0\), we can divide both sides by \(I_1^2\): \[R_1 = \frac{R_2}{4}\] This means the new resistance \(R_2\) is four times the original resistance \(R_1\): \(R_2 = 4R_1\).

Relationship between Resistance and Conductor Area

The resistance \(R\) of a conductor is given by: \[R = \rho \frac{L}{A}\] where \(\rho\) is the resistivity of the material (copper), \(L\) is the length of the conductor, and \(A\) is its cross-sectional area. For a 2-wire system, \(L\) is the total length (out and return) and \(A\) is the area of each wire (assuming both are the same). Since the power distance is the same, the length \(L\) is constant. The resistivity \(\rho\) of copper is also constant. So, \(R\) is inversely proportional to \(A\): \[R_1 = \rho \frac{L}{A_1} \quad \text{and} \quad R_2 = \rho \frac{L}{A_2}\]

Finding the Relationship between Areas

We found that \(R_2 = 4R_1\). Substitute the expressions for \(R_1\) and \(R_2\): \[\rho \frac{L}{A_2} = 4 \left(\rho \frac{L}{A_1}\right)\] Since \(\rho\) and \(L\) are constant and non-zero, we can cancel them from both sides: \[\frac{1}{A_2} = \frac{4}{A_1}\] This implies \(A_1 = 4A_2\), or \(A_2 = \frac{A_1}{4}\). The new cross-sectional area \(A_2\) is one-fourth of the original area \(A_1\).

Calculating Percentage Saving in Copper

The amount (volume or weight) of copper in the feeder is directly proportional to its cross-sectional area, as the length is constant. Let the original amount of copper be proportional to \(A_1\). Let the new amount of copper be proportional to \(A_2\). The saving in copper is proportional to the difference in area: \(A_1 - A_2\). Saving \( = A_1 - \frac{A_1}{4} = \frac{4A_1 - A_1}{4} = \frac{3A_1}{4}\).

The percentage saving is calculated as: \[\text{Percentage Saving} = \frac{\text{Saving}}{\text{Original Amount}} \times 100\%\] \[\text{Percentage Saving} = \frac{\frac{3A_1}{4}}{A_1} \times 100\%\] \[\text{Percentage Saving} = \frac{3}{4} \times 100\%\] \[\text{Percentage Saving} = 0.75 \times 100\%\] \[\text{Percentage Saving} = 75\%\]

Therefore, the percentage saving in feeder copper is 75%.

Was this answer helpful?

Important Questions from Distribution Systems

  1. Which distribution system is more reliable?

  2. Which of the following statements is INCORRECT?

  3. In a DC 2-wire feeder, the drop per feeder conductor is 2%. Find the transmission efficiency of the feeder.

  4. A 2-wire DC distributor cable 800 m long is loaded with 1 A/m. Resistance of each conductor is 0.05 Ω/km. Calculate the maximum voltage drop if the distributor is fed from both ends with equal voltages of 220 V.

  5. The fundamental difference between a transmission line and a feeder is that:

Need Expert Advice?

Start Your Preparation with Prepp Mobile App

Download the app from Google Play & App Store
Download the app from Google Play & App Store
Prepp Mobile App