A DC 2-wire feeder supplies a constant load with a sending-end voltage of 220 V. Calculate the saving in copper if this voltage is doubled with power transmitted remaining the same.
This problem explores the relationship between transmission voltage, current, and the amount of copper required for a DC 2-wire feeder when the power transmitted remains constant. The goal is to calculate the percentage saving in copper when the sending-end voltage is doubled.
For a DC circuit, the power transmitted (\(P\)) is the product of voltage (\(V\)) and current (\(I\)):
\[P = V \times I\]
Since the power transmitted (\(P\)) is constant in both scenarios, we can write:
\[V_1 I_1 = V_2 I_2\]
We know that \(V_2 = 2V_1\). Substituting this into the equation above:
\[V_1 I_1 = (2V_1) I_2\]
Dividing both sides by \(V_1\) (since \(V_1 \neq 0\)):
\[I_1 = 2I_2\]
This implies:
\[I_2 = \frac{I_1}{2}\]
So, when the sending-end voltage is doubled while transmitting the same power, the current flowing through the feeder is halved.
The saving in copper is directly related to the reduction in the cross-sectional area of the conductor required. In many practical applications, particularly when designing for thermal limits or maintaining a consistent current density, the required cross-sectional area of a conductor is considered directly proportional to the current it needs to carry.
Thus, we assume that the cross-sectional area (\(A\)) is proportional to the current (\(I\)):
\[A \propto I\]
This means the ratio of the new area to the old area will be equal to the ratio of the new current to the old current:
\[\frac{A_2}{A_1} = \frac{I_2}{I_1}\]
Substitute the relationship \(I_2 = \frac{I_1}{2}\) into the area ratio equation:
\[\frac{A_2}{A_1} = \frac{I_1/2}{I_1}\]
\[\frac{A_2}{A_1} = \frac{1}{2}\]
Therefore, the new cross-sectional area \(A_2\) is half of the original cross-sectional area \(A_1\):
\[A_2 = \frac{A_1}{2}\]
The saving in copper is the difference between the initial amount of copper and the new amount of copper required. Since the length of the feeder remains the same, the amount of copper (volume or weight) is directly proportional to the cross-sectional area.
Amount of copper saved \( \propto A_1 - A_2 \)
Substitute \(A_2 = \frac{A_1}{2}\):
Amount of copper saved \( \propto A_1 - \frac{A_1}{2} \)
Amount of copper saved \( \propto \frac{A_1}{2} \)
To find the percentage saving, we divide the amount saved by the initial amount and multiply by 100%:
\[\text{Percentage Saving} = \frac{\text{Amount of copper saved}}{\text{Initial amount of copper}} \times 100\%\]
\[\text{Percentage Saving} = \frac{A_1/2}{A_1} \times 100\%\]
\[\text{Percentage Saving} = \frac{1}{2} \times 100\%\]
\[\text{Percentage Saving} = 50\%\]
Thus, by doubling the sending-end voltage while keeping the transmitted power constant, there is a 50% saving in copper required for the feeder, assuming the conductor area scales directly with current.
| Parameter | Initial (\(V_1 = 220 \, \text{V}\)) | New (\(V_2 = 440 \, \text{V}\)) |
|---|---|---|
| Voltage (\(V\)) | \(V_1\) | \(2V_1\) |
| Power Transmitted (\(P\)) | Constant | Constant |
| Current (\(I\)) | \(I_1\) | \(I_2 = I_1/2\) |
| Cross-sectional Area (\(A\)) | \(A_1\) | \(A_2 = A_1/2\) |
| Copper Volume/Weight | Proportional to \(A_1\) | Proportional to \(A_1/2\) |
In a DC 2-wire feeder, the drop per feeder conductor is 2%. Find the transmission efficiency of the feeder.
What is the percentage saving in feeder copper if the line voltage in a 2-wire DC systems is raised from 100 V to 200 V for the same power transmitted over the same power distance and having the same power loss?
A 2-wire DC distributor cable 800 m long is loaded with 1 A/m. Resistance of each conductor is 0.05 Ω/km. Calculate the maximum voltage drop if the distributor is fed from both ends with equal voltages of 220 V.
The fundamental difference between a transmission line and a feeder is that:
Main consideration in designing of feeder is: