In a DC 2-wire feeder, the drop per feeder conductor is 2%. Find the transmission efficiency of the feeder.
Understanding the transmission efficiency of a DC 2-wire feeder is crucial in electrical engineering. This problem involves calculating the efficiency based on the voltage drop across the feeder conductors. A DC 2-wire feeder, as the name suggests, uses two conductors to transmit direct current power from the sending end to the receiving end.
In any power transmission system, there is always some voltage drop due to the resistance of the conductors. For a DC 2-wire feeder, power flows through two conductors: one for the supply (go wire) and one for the return path (return wire). The problem states that the voltage drop per feeder conductor is 2%.
Since it's a 2-wire feeder, there are two conductors contributing to the total voltage drop from the sending end to the receiving end. The total voltage drop is the sum of the drops in both the go and return conductors.
This means that 4% of the sending end voltage is lost as a drop within the feeder conductors.
The voltage available at the receiving end of the feeder (\(V_R\)) will be the sending end voltage minus the total voltage drop along the feeder.
So, the receiving end voltage is 96% of the sending end voltage.
The transmission efficiency (\(\eta\)) of a feeder is defined as the ratio of the power delivered at the receiving end to the power supplied at the sending end, usually expressed as a percentage. For a DC system, power (\(P\)) is calculated as voltage (\(V\)) multiplied by current (\(I\)). Since the current (\(I\)) flowing through the feeder is constant from the sending to the receiving end (assuming no loads tapped off in between, which is typical for such problems), the efficiency can be simplified based on voltages.
Substituting the value of \(V_R\) we found:
Therefore, the transmission efficiency of the DC 2-wire feeder is 96%.
| Parameter | Value/Formula | Explanation |
|---|---|---|
| Voltage drop per conductor | \(0.02 \times V_S\) | Given as 2% of sending end voltage |
| Total voltage drop (2 wires) | \(2 \times (0.02 \times V_S) = 0.04 \times V_S\) | Sum of drop in go and return wires |
| Receiving end voltage (\(V_R\)) | \(V_S - 0.04 \times V_S = 0.96 \times V_S\) | Sending voltage minus total drop |
| Transmission efficiency (\(\eta\)) | \(\frac{V_R}{V_S} \times 100\%\) | Ratio of receiving to sending voltage |
| Calculated Efficiency | \(0.96 \times 100\% = 96\%\) | Final efficiency value |
Which distribution system is more reliable?
Which of the following statements is INCORRECT?
What is the percentage saving in feeder copper if the line voltage in a 2-wire DC systems is raised from 100 V to 200 V for the same power transmitted over the same power distance and having the same power loss?
A 2-wire DC distributor cable 800 m long is loaded with 1 A/m. Resistance of each conductor is 0.05 Ω/km. Calculate the maximum voltage drop if the distributor is fed from both ends with equal voltages of 220 V.
The fundamental difference between a transmission line and a feeder is that: